Hello all:
I am interested in this forums opinions on the pro's and con's of "stabbing" wires into back of devices versus "screwing" down. As of now, our company use the screw method, but more and more over the years we are seeing this as the abnormal practice in our area.
Does it make since to continue to take the extra time to do this on our trim outs?
rick
|
|
|
|
Joined: Sep 2001
Posts: 806
Member
|
I have seen way to many poor connections and burned up wires to trust the backstab terminations. I always use the screw terminals, or better yet the screw down "pressure plate" type found on high quality devices.
|
|
|
|
Joined: Nov 2005
Posts: 827 Likes: 1
Member
|
I was taught not to back wire in the 70's. I have not seen anything to convince me that it is a good idea. When you twist the wire around the screw and tighten down, I think your contact area is a little more certain. Joe
|
|
|
|
Joined: Jul 2005
Posts: 49
Member
|
I love the "pressure plate" type termination. Back stab ease, but you still screw it down. Have found both backstab, and hook it and screw it down type devices burned up. I think if you avoid cheap devices, the termination style does not matter to a huge degree.
Pete
|
|
|
|
Joined: Feb 2005
Posts: 361
Member
|
Have you ever stabbed a breaker? I think that speaks volumes on the subject.
~~ CELTIC ~~ ...-= NJ =-...
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
celtic: How about those horrible Zinscos with the quick release? I think I have a few in my junk pile.
Stupid should be painful.
|
|
|
|
Joined: Apr 2003
Posts: 362
Member
|
I personnally love the stab in the back................they keep me in business. Garuanteed service calls in the waiting. Usally the 1st device on the circuit stab fails when the load side devices are loaded up. Space heater on the last device and a couple of lamps and boom a service call for no power, power keeps going on and off, burned device, open neutral, etc. Ob
Choose your customers, don't let them choose you.
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I think a sure fire way to make a stab fail is to have the wire less than perfectly straight when you stab it.
Greg Fretwell
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Have you ever stabbed a breaker? Yes. Somewhere on this site I have a picture of a QO twin breaker with speedwire terminals.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
quote:Have you ever stabbed a breaker?
Yes.
Somewhere on this site I have a picture of a QO twin breaker with speedwire terminals. Iwire Say it aint so. QOs with back stabs. That's it the world has officially gone to hell. -- Tom Horne
Tom Horne
"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
|
|
|
Posts: 2,236
Joined: November 2000
|
|
|
|
|