rhpope Offline OP
Ihave a dry type 3-phase distribution tranformer with the following specs:
45 KVA
HV: 208Delta V
LV: 220Y/127 V
How do you get 208V Delta? Is this just the three phases of 208Y/120 V brought in without the neutral? What would be the typical application of such a small voltage increase? Would this be considered an isolation transformer?
[This message has been edited by rhpope (edited 04-03-2006).]
"Is this just the three phases of 208Y/120 V brought in without the neutral?"
That would be the result; 208v line-to-line.
"Would this be considered an isolation transformer?"
More likely a neutral-deriving device. Here's why I say that: (208/220)*127 = 120
It seems that the function of this transformer is to restore a "lost" neutral, or perhaps a way to provide an isolated (floating) neutral.
Larry Fine
Fine Electric Co.
fineelectricco.com
Thinking further, it could be a 208-to-220v step-up, instead of using buck-boosts.
Larry Fine
Fine Electric Co.
fineelectricco.com
Larry, I am guessing a buck-boost right now also...
But don't know without seeing the nameplate..
And if it is, you don't need the nuetral on the Hv side, just the 3 phases..
Never seen a use for a 208-220 3 ph transformer, but I am sure there is one. Is this used on a machine that needs isolation?
Dnk..
[This message has been edited by Dnkldorf (edited 04-03-2006).]
I use a 208V delta to 277/480V wye transformer to separately derive a neutral for an isolated system in my lab.
-Jon
Definitely sounds like a Voltage Boosting setup here - in the form of an Isolated Transformer, rather than the more commonly used "Brute Force" approach with Autotransformer connected 1 Ø Transformers.
The Primary Windings are connected as a Closed Delta 3 Ø 3 Wire arrangement - as is common with many 3 Phase Low Voltage Dry-Type Transformers.
The Secondaries are connected as a Wye, with provisions to land a Common Conductor to the Star Point via Terminal "X-0"
The Primary Windings of the Transformer mentioned in this thread, are wound for an input Voltage level of 208 VAC nominal, and are simply connected in Parallel to each other - resulting in a Delta configuration.
Scott35