Joined: Dec 2004
Posts: 1,064
D
Member
How would size these if the PF changes from .62-.78 depending upon the load?

The highest reading I took during a 3hr test was .84. Would you calculate it at the highest reading or average it out?


Dnk...

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Is the customer being bill for a KVA demand?
You would size the caps based on the max demand and PF. Suggest you contact the utiltiy and get the max demand from them.If the PF is 0.84 I would try to improve it to
0.98 or something close depending on the size of the caps rrequired.

Joined: Apr 2004
Posts: 349
Member
Dnk - Rather than calculating based on min, max or average, I think I'd try to figure out what the nominal PF is, I mean what is the prevailing PF reading most of the time. It might be dificult to ascertain, but it seems to me that if you correct for that level, then the amount of time of over correction and under correction will be minimized, and the amount of time of 'just right' correction will be maximized.

Radar


There are 10 types of people. Those who know binary, and those who don't.
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Radar
Thats one way of doing it. However if you are being billed for the max KVA demand that method will cost you money.

Joined: Apr 2004
Posts: 349
Member
OK - I can see that. That being the case, should we figure out what the PF is while at max KVA demand and correct for that?

Radar


There are 10 types of people. Those who know binary, and those who don't.
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Radar
That is correct. The utility can tell you what the KVA demand and PF is. You can then caculate the required capacitors to correct the PF to say 0.98 or 0.99.

Joined: Apr 2004
Posts: 349
Member
OK Bob - let me ask another question here (I feel like we're leaving Dnk outta this). Your first question was whether the customer is being billed for KVA demand. What if they weren't, would we then be back to what I said earlier about figuring out the PF that takes the largest amount of time and correct for that, recognizing we'd be over correcting or under correcting at other times? Hopefully we'd be covering a major portion of the day with close to 1 correction.

Or would we still figure the hishest KVA demand and correct for that? Or would we simply forget the whole thing altogether if the poco is not billing for KVA demand?

Radar


There are 10 types of people. Those who know binary, and those who don't.
Joined: Dec 2004
Posts: 1,064
D
Member
Radar, you're not leaving me out of anything....

I am reading everything you guys say, and learning. I have more input, but I am waiting to hear responses to kinda formulate my next post...

I agree to what Bob is saying, however my readings were taken off a subpanel, @ 250' away from the service. Somehow I think I need to contact the power company, and do a whole plant survey with readings from the service to each subpanel, draw a line diagram and possibly correct in different areas rather than a bulk correction at the service entrance....

The sub panel is a 400A 480v panel. The customer is a huge machine shop.

What is your guys take on this idea?

Dnk..

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
If the customer is being billed on a KW demand then there is no need to install the caps. They won't reduce the demand charge.

Dnk
If the main is only a 400 amp I doubt that there is a KVA demand. Probably a KW demand.
If there is a KVA demand charge, I think installing the caps at the main will be a cheaper installation. How did you measure the PF at the panels?

Joined: Dec 2004
Posts: 1,064
D
Member
Bob, service is 1200A 480V. That was just a subpanel reading.

Would correcting PF reduce line losses?

Fluke 434B (3) phase analyzer..

Dnk..

[This message has been edited by Dnkldorf (edited 02-24-2006).]