The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
Yesterday at 11:37 PM
Housekeeping and Clean-up
by renosteinke
Yesterday at 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
Which bright spark can help me here?
by LarryC
05/20/12 11:20 AM
100AMP panel in 60 degree ambient what size wire?
by twh
05/19/12 07:21 AM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
HotLine1 29
gfretwell 27
sparkyinak 17
twh 15
renosteinke 15
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 90 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129516 - 04/05/05 05:28 PM motor disconnect question
knopp Offline
Junior Member

Registered: 06/26/04
Posts: 2
Loc: richmond, va
i have two 480 3 phase motors, the first is a 10HP (14FLA)and the second is a 30HP (40FLA) these two are to be fed from individual circuit breakers at a main lug panel and a fusible disconnect supplies the incoming power. how do you properly calculate for the correct size time delay fuses at the disconnect.

Top
#129517 - 04/05/05 07:29 PM Re: motor disconnect question
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
How about 430.63, which would, in your case put you at 430.62?
40A x 175% = 70A
70A + 14A = 84A
84A + the lighting and appliance load on the panel = Time Delay Fuse size?

[This message has been edited by Redsy (edited 04-05-2005).]