The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
Yesterday at 11:37 PM
Housekeeping and Clean-up
by renosteinke
Yesterday at 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
Which bright spark can help me here?
by LarryC
05/20/12 11:20 AM
100AMP panel in 60 degree ambient what size wire?
by twh
05/19/12 07:21 AM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
HotLine1 29
gfretwell 27
sparkyinak 17
twh 15
renosteinke 15
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 90 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#129193 - 09/29/04 10:09 AM Leakage Capacitance
Electra Offline
Member

Registered: 07/29/02
Posts: 38
Loc: Portland, Oregon, USA
Soares Book on Grounding mentions that an ungrounded system is capacitively coupled to ground and the existance of leakage capacitance. I understand what capacitance means, but can anyone explain to me what the actual physical implications there are on the system due to this leakage capacitance. Also, why is this not such of an issue on a grounded system????

Thanks,

Laura J

Top
#129194 - 09/30/04 08:06 AM Re: Leakage Capacitance
JBD Offline
Member

Registered: 07/12/01
Posts: 536
Loc: WI, USA
Trying to keep it short and simple, so ask for more details if you want.

All AC systems have a natural capacitive coupling to ground. In a balanced system the associated leakage current cancels simialr to the way the balanced phase currents cancel. But if one of the phase conductors is grounded then there is no canceling of the charging current.

In a low resistance grounded wye system the overcurrent protective devices should operate when a phase goes to ground preventing further problems. However in high-resistance grounded wye systems the OCPD will not open causing the charging currents form the other two phases to increase by a factor of 3 (this is caused by the change of the phase angles and the increased voltage to ground).

The charging current in a high resistance ground system is minimal so even a 3 times increase is not usually a safety hazard. The primary reason we are concerned at all has to do with the settings and operation of protective realys and other ground monitoring equipment.

Top
#129195 - 09/30/04 09:25 AM Re: Leakage Capacitance
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
 
To effectively damp phase-to-ground overvoltage in an ungrounded system (with complete equipment grounding and bonding in place) the capacitance between phases and ground must be damped by a resistor connected from neutral-to-ground.

“Charging current” for 480V systems is roughly 1 Ampere/1,000kVA of system capacity. [In the case of delta systems, the neutral has to be derived from zig-zag or wye-primary—delta-secondary transformers.]

Here is my favorite story about the very serious problems that can occur with low-voltage ungrounded distribution.




[This message has been edited by Bjarney (edited 09-30-2004).]