#129025 06/23/04 10:58 PM
Joined: Apr 2004
Posts: 349
Member
To summarize, there are 2 flavors of a 240V Delta:

240V 3-Phase 3-Wire (Straight delta)

120/240V 3-Phase, 4-Wire (Hi-Leg Delta)

----------------------------------------

The 208 Volts that coincidentally exists between phase B and neutral (the ki-leg) is NEVER usable. No 1P CB's on phase B.

Radar


There are 10 types of people. Those who know binary, and those who don't.
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#129026 06/23/04 11:18 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Other comments from E-C.net members are welcomed if you see this as inappropriate advice...

Given no grounded-circuit conductor from the serving transformer connected to a neutral bus in the three-phase panel, it is not usable in 4-wire delta service, and not intended to serve 120V branch circuits. In basic terms, a 240V-primary transformer is needed to furnish 120/240V 1ø 3w (connected to two phases in the 3ø panel.)




[This message has been edited by Bjarney (edited 06-24-2004).]

#129027 06/24/04 04:37 PM
Joined: Dec 2001
Posts: 201
A
ayrton Offline OP
Member
That makes sense BJarney. A grounded conductor was pulled with the three phases.
Phase to phase is 240v Cphase to ground is in the 208 neighborhood.
I was confused with the xfmr installation in the beginning because I wasnt 100% on the Delta. It is clear now the other sparky wasnt either.
Most installations I see are 4wire w/ high leg.
Some reason though they only pulled a #2 with the 500's for Grounded conductor. Really limits the single phase circuits unless size is upgraded.