The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
Yesterday at 11:37 PM
Housekeeping and Clean-up
by renosteinke
Yesterday at 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
Which bright spark can help me here?
by LarryC
05/20/12 11:20 AM
100AMP panel in 60 degree ambient what size wire?
by twh
05/19/12 07:21 AM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
HotLine1 29
gfretwell 27
sparkyinak 17
twh 15
renosteinke 15
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 90 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Page 2 of 2 < 1 2
Topic Options
Rate This Topic
#128905 - 07/23/04 06:57 AM Re: solid state flame control and generator
chi spark Offline
Member

Registered: 01/06/04
Posts: 102
Loc: Chicago IL USA
Hi- the flame circuit needs to read a ground path through the flame-which is flame rectification. this is a mA circuit that, when not present whether because of a poor ground or a dirty sensor, will present itself exactly as you describe-3 tries and a lockout. this sensor usually resembles a spark igniter electrode and is at the opposite end of the burner assy. from the igniter. While the unit is on the grid, you could disconnect this sensor and see the same behavior. That being said, there must be something about the gen-sine. Perhaps a small ups/conditioner would do upstream from the control board, so it wouldn't need to be sized for the fan motor. Have you checked the frequency of genset output?

Top
#128906 - 07/23/04 07:43 AM Re: solid state flame control and generator
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
"High speed" {sub-cycle} voltage changes cannot reliably be measured with a voltmeter. That's what oscilloscopes and related power-quality instruments [and consequent bird-dogging] are for.

Top
#128907 - 08/23/04 03:14 AM Re: solid state flame control and generator
Frank Martino Offline
New Member

Registered: 05/04/04
Posts: 7
Loc: Middlebury, CT, USA
I suspect that a ferroresonant transformer will have a faster response time than a furnace and should resolve the problem. The advantage over a UPS is that the transformer doesn't need the maintenance of that a battery requires.

<< A ferroresonant transformer, also called a constant voltage transformer, will give a constant AC voltage output when the input voltage varies within the rated input voltage range. Typical response for output regulation is plus or minus 3% for input voltage swings that are within the rating of the transformer. Typical response times are 8 millseconds for a 5% line or load variation, and 16 milliseconds for a 10% variation. Generated harmonic distortion will be less than 3%. >>
http://www.powerqualityanddrives.com/sag_correction_without_ups/