Scott (or anyone else): I glanced through you very informative technical resource area, but I could not find any examples of short circuit/fault current calculations. Would you mind showing me an example of one when you find the time? Thank you very much.
Ryan Jackson, Salt Lake City
One simplified calculator is listed at http://www.bussmann.com/apen/software/ Available short-circuit currents are primarily controlled by various transformer impedances in power systems, which also cause voltage drop in AC-electrical circuits.
Posts: 2,723 Likes: 1
Broom Pusher and Member
SCA calcs (formulas) were something I should have compiled and posted in the Reference section, but strangely enough have yet to do so! I'll see what can be compiled from the Bussman SPD documents for the three commonly used methods, then post ASAP. Scott35
Scott: Thanks. Again, at your convienance. I hope I didn't come across as complaining about your very informative section, that was certainly not the intent. Bjarney: Thanks. I have reviewed the site and found it quite helpful
Ryan, As a rule, PSCC(Prospective Short Circuit Current) is governed by this formula, as a very simplistic way of looking at it: I(pscc)= V(oc) / Z.
[This message has been edited by Trumpy (edited 01-05-2004).]
Easiest way is ignore primary and secondary conductor impedances since the transformer impedance is usually quite large compared to the wire impedance. Then it's just Ohm's law, I = E/Z, or I = (1/%Z)(FLA).
In other words, just divide FLA by Transformer PU impedance(%Z/100)
Example: For a typical 25 kva, 12kv to 120/240v transformer, Z% = 2.4%. I (SC) = 104.2/.024 = 4340A
BTW, some new pole mounted and some padmount transformers have impedances less than 2 percent.
There are different method of calculating short circuits. It depends what component are installed on the system.
One book that help me a lot, whem I am doing short circuit calculation is
"Electrical System analysis and design for Industrial Plant by Irwin Lazar".
The examples are very easy to understand and very applicable to modern electrical system that exist today.
Here's some "Quick 'N Dirty" SCA calc formulas, using the basic "Point-to-Point" method.
Available short-circuit symmetrical RMS current is found using the 6 steps described below:
Step 1; Determine the Transformer's Full-Load Amperes (I·fl):
3Ø Transformer
I·fl = KVA × 1000 / E·l-l × 1.732
1Ø Transformer
Step 2; Find the Transformer multiplier (M·tr):
M·tr = 100 / (%Z × 0.9) where: %Z is the Transformer's Impedance.
Step 3; Determine the Transformer let-thru short circuit current (I·sc):
I·sc = I·fl × M·tr
FYI: Induction Motor contribution may be added to the above figure at this point. An estimate for Motor contribution to SCA is: 4 to 6 × FLA of Motor(s). LRA may also qualify.
Step 4; Calculate the "F" factor:
3Ø Faults:
F = 1.732 × L × I·3ø / C × E·l-l
1Ø L-L Faults on 1ph center tapped transformer:
F = 2 × L × I·l-l / C × E·l-l
1Ø L-N Faults on 1ph center tapped transformer:
F = 2 × L × I·l-n / C × E·l-n
where: "L" = Length (feet) of conductor to the fault. "C" = Constant from "Table C" of the Bussman manual (will add this later - big database!). "I" = Available short circuit current at beginning of circuit. "L-L" = Line-to-Line. "L-N" = Line-to-Center Tapped "Neutral" conductor. *Note: L-N fault current is higher than the L-L fault current at the secondary terminals of a 1Ø center tapped transformer. The short circuit current available for this case in step 4 should be adjusted at the transformer terminals as follows: I·l-n = 1.5 × I·l-l at transformer terminals.
Step 5; Calculate "M" (multiplier):
M = 1 / 1 + F
Step 6; Calculate the available short circuit symmetrical RMS current at the point of fault (I·afc):
I·afc = I·sc × M
I'll post a few example SCA scenarios later when posting the "C" database.