#128407 02/24/03 02:27 AM
Andre M Offline OP
Problem recently posted for my class:
Heating element rated 240v 4800W (20A) has been connected to 120/208v grounded "Y" system between two phases (208v). - Everybody egrees now 3600W / 17.3A.
1. Midpoint of the element is shorted to ground assuming 0 (zero) resistance of ground fault. What total power is rreleased during ground fault?
2. What current flow to ground?
What is your opinion on asked numbers? - Is it too hard for master electrician?
Andre
#128408 02/24/03 08:46 AM
Gwz Offline
Find ohms of the original.
R = E / I, R = 240V / 20A, R = 12 ohms.
Now this is used on a 208/120V system.
The Neutral of 208/120V system is intentionaly connected to Ground and you noted 0 restistance to ground, thus the circuit at midpoint is being operated as on 120V system.
1/2 of the 12 ohms is 6 ohms.
I on the 120v as now operating is;
I = E / R, I = 120V / 6R, I = 20A on each of the two sections of the ground faulted 240, 4800W, 20A heater operated on the 208V system.
#128409 02/24/03 10:05 AM
Andre M Offline OP
Yes, thanks. Now a little harder second question. Find ground current.
#128410 05/25/03 06:48 AM
20 Amps.
Ichabod
#128411 05/31/03 10:00 PM
Should I draw this one up and post it in the Tech. Reference section?
Scott
#128412 06/01/03 09:36 AM
Yes Scott, please do.
Ichabod
