Scott35 Online Happy OP
This topic contains several Images of High Voltage DC Transmission circuits, plus some descriptive text.
Thanks to ECN Member Bjarney for contributing these Images and information!!!
If you have Q's or comments, feel free to post 'em!
Scott S.E.T.
Now, to the pics!!!
Pacific DC Intertie from Northern Oregon to Southern California
Image #1: High Voltage DC Transmission lines
Image #2: High Voltage DC Transmission lines
Image #3: HVDC lines - note the 3 Phase High Voltage AC lines behind the HVDC lines
Image #4: HVDC lines - note the 3 Phase AC lines again
Below I have attached some "Snipped Text" about these Images and types of systems
(Text also from Bjarney):
<snip>
Three-phase AC power is fairly universal all over this planet, but occasionally there are deviants.
A few pictures of DC-power lines, rated at ±500kV 3100 amperes.
At its ends there are converters to 230kV 3ø for "local" use.
Converter stations: Celilo / Sylmar
One western-US circuit is ±500kV. Line rated at 3100 amperes and {ha!} 3100MW.
Under a pole-outage condition, by treaty-the nodes can be run with a ~1600-ampere earth return for up to 20 minutes-primarily in deference to telecommunications interference.
Transfer capacity is significantly constrained in this mode, but is operable.
Earth return seemingly creates very interesting problems. Return-current polarity changes based on which pole has failed. Ground electrodes of cast iron are located in marsh at the north, sea at the south.
<snip>
end.
[This message has been edited by Scott35 (edited 10-06-2002).]
one would assume this especially so for the particular inhabitant of said 'earth'.....