ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 636 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 3 of 3 1 2 3
Joined: Nov 2000
Posts: 2,148
R
Member
Mark,
All three grounded conductors are connected together. The only difference in the current on any of the conductors will be based on the impedance of the path. There will only be very small differences in the impedances and therefore only a small difference in the current flowing in each grounded conductor. I agree that you will have little current in the grounding electrode conductor between the last panel and water pipe. Take an example of a condition where there is 50 amps of unbalanced current in panels 1 and 3 and 20 amps in panel 2. In this case you would have 10 amps on the grounding electrode conductor from 1 to 2 and from 3 to 2 but each grounded conductor would have 40 amps. If the unbalanced current was 60 on panel 3 and 0 on the other 2 panels, you would have 40 from 3 to 2 and 20 from 2 to 1. Unless there is a problem with one of the grounded conductors between the transformer and the panels, the grounded conductors will never be over loaded.
Don(resqcapt19)

[This message has been edited by resqcapt19 (edited 03-16-2002).]


Don(resqcapt19)
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2001
Posts: 280
M
Member
Don:
I think I have finally described it correctly, as you said whether the two copper are bonding jumpers or not doesnt matter. Now back to my original question. The jumpers between these three panels do carry current, this is the way we are to tie the three of them together, I just dont like the idea of these conductors carrying current. When a Meter/Disconnect is used this is not a problem.
As with wiring to a separate building that has a metal piping system common to both buildings a 4 conductor must be run to prevent Neutral currents from flowing on the grounding conductor thus creating a ground-neutral voltage.
I would like to know too, how you got the proportions of the current distribution in the example you used ?

Thanks again
- Mark