1 members (Scott35),
494
guests, and
11
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
Ok, We all know 2 X-formers and 3 hots can do an open delta, but....... Can 3 X-formers and 2 hots be configured into some sort of 3 phase arrangement? According to one source , this is called a 'scotch-something...'
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
You are referring to a Scott connected configuration, in which a 3 phase primary is connected to two transformers in such a manner that 2 phase power is availableon the secondary. This information is available in McGraw-Hill's "American Electricians Handbook"
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
hmm; i see it in the index, but not in the book, go figure....
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Originally posted by sparky: hmm; i see it in the index, but not in the book, go figure.... Sparky, What edition do you have? I'm home and my 11th edition discusses this beginning on page 5-55. There is a diagram on page 5-57. When I go in tomorrow, I'll check my other(newer) edition.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
well I have a 13th, the index says it's at 5-92 to 5-94, which is just a lot of stuff about drying X-formers
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Originally posted by sparky: well I have a 13th, the index says it's at 5-92 to 5-94, which is just a lot of stuff about drying X-formers I have the 13th, also. The index is confusing. It refers to sections, not pages. Look at SECTION 5-92 on PAGE 5.67
|
|
|
|
Joined: May 2001
Posts: 717
Member
|
Designed to replace the Edison 3 wire DC hook up when swapped over to AC. Unless you work around coal mines (DC equipment runs on AC or batteries) you'll never see one. coal mine info is old, don't know if they still do it that way.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
Look at SECTION 5-92 on PAGE 5.67Dohh! Homer Simpson....Ok, so I can't use my own book! anywho, there it be, stange animal that it is. Could this be used in reverse? I.E.- get 3 phase 208V out of 2--4160V high legs? that was the description I got from my 'source'
|
|
|
|
Joined: Jul 2001
Posts: 599
Member
|
According to my engineering books the Scott connection is normally used for 2-phase to 3-phase conversion. If used in a 3 to 2 conversion the transformer output needs to be reduced to 86.6% of the combined single-phase ratings.
|
|
|
|
Joined: Oct 2000
Posts: 5,392
OP
Member
|
JBD, can you elaborate? the particular situation here was a linesman stating that 2 out of 3 phases were available at a job, and 3 ph was created via this 'Scott' configuration.
|
|
|
Posts: 43
Joined: September 2013
|
|
|
|