ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Electricians revenge
by gfretwell - 05/09/24 08:24 PM
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 128 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jul 2001
Posts: 311
F
Member
A particular emergency lighting unit (battery pack) is rated for 100 watts. Remote lighting heads will also be fed. The voltage is 6VDC. I'm trying to understand "amp hours" which I see listed on replacement batteries for emerg. lighting units. For this 100 watt unit, how many amp hours should the battery (batteries) be rated for?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

A
Anonymous
Unregistered
100 watts @ 6 V for 1 hour is 16.67 A·hr.

If your actual wattage is 50, a 16.67 A·hr battery will last two hours.

What is your actual wattage and how long do you want them to remain fully lit?

Joined: Jul 2001
Posts: 311
F
Member
eg. 75 watts for 90 minutes.

A
Anonymous
Unregistered
75 W <= 100 W

75 W @ 6 V = 12.5 A

12.5 A * 1.5 hr = 18.75 A·hr

Joined: Jul 2001
Posts: 311
F
Member
Thank you. I now understand.

Joined: Mar 2001
Posts: 2,056
R
Member
One other thought -- I remember reading that the amp-hour relationship is non-linear.
A 10 amp hour battery will deliver 1 amp for 10 hours, but will not be capable of delivering 10 amps for a full hour.

A
Anonymous
Unregistered
Correct. That's why it is important to note that his 75 W load is less than or equal to the 100 W rating of the battery. If he had a 200 W load, it would severely underperform. If he had a 10 W load, it would significantly overperform.

Joined: Jul 2001
Posts: 311
F
Member
I'd like to give one more example. A 36 watt, 6VDC emergency lighting unit has it's battery missing for one reason or another. I would order a 9 amp hour battery based on the actual wattage (36) fully lit for 90 min. Am I correct?


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5