ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#127424 07/02/01 03:19 AM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Scott35 Offline OP
Broom Pusher and
Member
[Linked Image]

This Schematic shows how to find relative polarities of Primary and Secondary Windings on a 1 phase 2 wire Transformer.

The "Test Jumper" shown [connecting the Primary and Secondary Windings at one end], is used only for this test.
Using a common DVM [Digital Voltage Meter], check the voltage between Primary and Secondary - as shown and represented by the "E" in the circle.

Any comments???

Scott SET - posted 07/02/01


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#127425 07/03/01 03:59 PM
A
Anonymous
Unregistered
> [connecting the Primary and Secondary Windings at one end], is used only for this test.

I want to thank you big time for pointing out that the primary input can be used as a reference voltage.

#127426 07/07/01 05:36 PM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Scott35 Offline OP
Broom Pusher and
Member
Dspark,

Happy to assist!!!

In this scheme, the setup is very much an Autotransformer, which is derived with the "Test Jumper" connection between primary and secondary.

So the results will be either:

<OL TYPE=A>

[*]Primary Voltage + Secondary Voltage = Output Voltage; for "In-Phase" additive polarity, or

[*]Primary Voltage - Secondary Voltage = Output Voltage; for "Out-Of-Phase" subtractive polarity.
</OL>

*** NOTE *** Output Voltage is what's measured at the Voltmeter "E"

As you have said here, the primary can and is used as a reference voltage.
If the transformer was rated for 200 VAC on the primary, with a secondary voltage of 20 VAC - this would need to be kept within tolerances in order to correctly reflect the Impedance [Z] of the secondary's load.
If 1/2 the voltage, or 100 VAC was applied to the primary, the secondary will be effected - possibly as far as 1/2 the secondary voltage, or only 10 VAC available in the secondary.
This applies to all transformers.

A Power-type transformer will work in the basic fashion of a typical Impedance matching transformer - which "reflects" a different connected Impedance to the supplying source, than the actual connected Impedance.
Example:
If the connected load on the secondary would be 10 ohms Z, and it was rated for either 10 VAC or just 1 amp [or both], and the voltage available is 100 VAC, we cannot simply connect the 10 Z load to the 100 VAC supply and expect the smoke to remain inside!!!, so we connect it thru a Transformer - which makes the 10 Z secondary load appear as a 1000 Z load to the power supply.
Now the power [in Volt-Amps] can be applied as needed; 10 VA on the primary [supply], 10 VA on the secondary [load]. 100% power transfer - except minimal transformer losses and such.

Thank you for the reply!!!

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!