538
30
Posts: 3,682 Likes: 3
Administrator Member
What is a "Pringle switch"? BTW, How long did they take to restore power?
Posts: 869 Likes: 4
Amazing !!
LV faults near high capacity transformers 1 or 2 MVA or bigger have enormous amounts of power and destructive capacity as seen in these photo's.
Someone would have been very shaken and needed to change some un%$^s when closing that switch.
~~ CELTIC ~~ ...-= NJ =-...
Only one comment, Glad no one got hurt and WOW
What did the pringle switch look like after this "event"? I know virtually nothing about this type of switchgear. Is PPE required for someone operating this equipment (or at least a real good idea)?
[This message has been edited by mamills (edited 10-11-2006).]
The plant has several Pingle switches.Most of them were installed mid 70s to late 80s. We have then on a RM program and we clean and lubricate the blades of the switches. We found that if you dont RM they may not open porperly. Ours are fused switches not electricaly operated . Pringles switches are bolted pressure contact switches and when the knives contact the stationary contacts they actualy have a cam on each knife that generates additional force to help ensure greater contact pressure. To those who have not seen a Pringle switch they look like a custom made device not something mass produced a lot of pride goes into them.
VAelec:
What was the cause of this failure, or are you not at liberty to say?
"Violent" is too small a term for this one.....
Stupid should be painful.
480V 4000A AL Duct in a 14 story building in Arlington, VA. Pringle switch tripped and was reset and a fireball consumed a good portion of the 14th floor. I'd venture to say they had two major failures. I think the first more obvious than the second...
