Individual runs of copper water pipe? That's crazy!
Those also look like custom made fuses. It looks like the ratings were probably hand stamped on them. Those are pretty cool, so long as theyre used properly
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
Don't think that's water pipe, but a metal-encased, mineral powder filled (as insulation) cable. I forget the tradename, but there was a thread about it on here somewhere....
Stupid should be painful.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Pyrotenax.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
In the NEC it is called MI Cable.
It is fireproof (more or less) it can operate even while sections of it are exposed to open flame.
A typical use of it is for life safety emergency circuits.
The insulation between the copper conductor and the copper sheath looks like Sheetrock and is somewhat flexible until exposed to high heat than I believe it turns hard more like ceramic.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2005
Posts: 869 Likes: 4
Member
|
or MIMS
Mineral Insulated Metal Sheethed
The product of rotation, excitation and flux produces electricty.
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
Just an off the wall question but do you think they used this type of conductor because it basically runs unfused from the service head ( between the 2nd and 3rd floors) down to the sub basement where the disconnect is located... I assume they would have to have buried it in the masonry and concrete slab for protection?!?! Doesnt seem correct, but thats how it was done 40+ odd years ago.
A.D
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Here is the thread where MI (pyro) cable was discussed. {Message edited to fix tag} [This message has been edited by Trumpy (edited 08-21-2006).]
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
Very cool! I will be definately looking up more information on pyro cables. That is the first time I have actually seen it installed and in service. Too bad its not too popular here any more, I would have really liked to get lessons on how to properly install pyro and get some hands on experience installing the stuff.
A.D
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
It looks like the lock nuts on the MI connectors are ferrous. That could be a problem. It apprears that the 3 MI connectors enter the enclosure via some type of plate that is bolted to the inside of the enclosure. I assume that is nonferrous to pevent induction heating. Don