This kind of looks like the results from one of the following scenarios:
<OL TYPE=A>
[*] The Barbecued item was a 2 pole Breaker, which had the Panelboard's Feeders brought into it, and the Feeders were loose in the lugs,
[*] BBQ'd device is 2 Pole C/B, which had loose terminations on the Bus slots,
[*] BBQ'd device is a lug assembly, which mounts to the Bus Kit, which had loose terminations to the Bus - or loose Feeder terminations on the lugs,
[*] Being that the Feeders are Aluminum, maybe someone came along in the past few Years and "messed around" with the terminations - maybe going as far as terminations which had oxidation and/or not using any Anti-Oxidation compound.
</OL>
Those little Federal Pacific "Panel-ettes" can become extremely dangerous after being opened a few times (namely, by unexperienced personnel).
If they are "Untouched", the Breakers remain tightly seated inside, and there is very little heat "generated at the Panelboard"
After someone with little to no knowledge of the FPE line (or what occurs when Bus Terminations are left loose) gets in these Panels, the trouble starts.
First common problem is the dead front cover doesn't fit back on properly, so instead of correcting the problem where it exists (the enclosure is tweeked, due to the installation of a new circuit), the cover gets bashed back on - ultimately resulting in damaging a Breaker, loosening them from the "Stab-LoK" Bus, or both.
Second, someone installs an incorrect style FPE breaker on the Bus, which ends up being loose on the Bus - transferring built up heat to the Bus and all Breakers in it's proximity.
I am not saying the FPE "Stab-Lok" line is all that great; only that these are kind of like K&T Wiring:
When some unexperienced person messes with them, trouble usually starts immediately afterwards.Have dealt with "a few" panelboards in my career, and have also seen "a few" unexperienced persons work on panelboards, which - in a wierd way - assisted in my overall experiences, understandings and knowledge.
This is why I prefer to excel in Broom Pushing!!!
Scott35