1 members (Scott35), 216 guests, and 11 robots.
#12347 08/08/02 01:03 AM
Cindy Offline OP
egc = equipment grounding conductor
residential kitchen, small appliance bc in 2 gang box with switch leg for light..... crimp sleve the egc'c for both, or keep them separate? why?
also is there a code restriction to not cut off one of 2 tails from an egc crimp sleve? or is just one tail ok for the device? thanks
#12348 08/08/02 07:43 AM
bc = ????
#12349 08/08/02 08:15 AM
branch circuit=bc???
just joes guess here small appliance branch circuit
Lighting the way
#12350 08/08/02 08:36 AM
Still no decoder ring...
All equipment grounds in a box are to be bonded (spliced) togther, even if they are on different circuits. This is NOT to be mixed up with noodles, for they should remain independant from other circuits.
Even though it isn't widely enforced, the 6" free conductor length also applies to EGC's, so the shortest one has to be 6" (with 3" available outside the box).
Sorry, book's in the truck, I'm lazy this morning, so no code refs...
-Virgil
5 Star Inspections
Member IAEI
#12351 08/08/02 08:38 AM
Cindy,
250.148 tells me that all EGCs must be joined together.
With multiple devices in a box, leaving the multiple tails on the EGCs makes it easy to ground the devices.
#12352 08/08/02 08:46 AM
joeh20,
Good Call!
I was wondering about 'bc' myself.
#12353 08/08/02 09:42 AM
Cindy,
As to the "why" for tying the egc of one circuit to another (or others). . .this creates multiple parallel return paths for fault current. The egcs form a net or web. The overall resistance of the egc is reduced by the parallel resistances.
Al
Al Hildenbrand
#12354 08/08/02 03:14 PM
I use Buchan spice caps for the EG. Slide the cap over long ground leads (after twisting them together). Leave one lead for each device and if it’s a metal box leave one for that also. Then cut off the remainder.
Also on rough in, I like to group the leads for each device and do a “barber pole” wrap with the ground wire.
#12355 08/08/02 09:27 PM
Cindy Offline OP
sorry, i must be the worst at over-using abbreviations here
some tie all egc's together, and some only tie the 12awg's together and put the 14awg's together in separate crimp sleeves, 250.148 seems to say all egc's are to be tied together, but it says "where circuit conductors are spliced" so i guess they could argue that it doesn't say "where DIFFERENT[12awg, 14awg] circuit conductors are spliced" they have to be spliced together. so if all ciruits with egc's in a plastic box are required to be spliced together, why doesn't it get turned down by inspectors? i just saw this today.
Al, thanks, that's a different way of looking at the parallel path idea for me. i always thought of parallel paths as bad things.
about the decoder ring thing.
maybe over in the left margin with the advertisements we could have a quick easy reference decoder ring listing of abbreviations of the top ten or so, think of all the bytes we could save [Linked Image] my votes are for these.
GEC grounding electrode conductor
GC grounded conductor
UGC ungrounded conductor
EGC equipment grounding conductor
BC branch circuit
OCPD overcurrent protection device