0 members (), 331 guests, and 10 robots.
#123023 02/20/06 12:30 AM
Trumpy Offline OP
Yet more pics from RODALCO:
End termination pole. 11 kV cockroach, from Waiwera, rural line mostly 25 or 35 mm² Copper:
RMU(Ring Main Unit), for 600 kVA dry transformer for mining auxillaries:
SDAF 11 kV cables, 2 days before livening. Backfilled with sand on the day of "switch on":
11 kV incoming supply to RMU in local tunnel sub:
SDAF bank:
#123024 02/20/06 12:39 AM
Trumpy Offline OP
And more:
LV side 250/433 Volts transformer, 600 kVA for auxillary supplies:
RMU data, Merlin Gerin Ringmaster:
LV side 240/415 Volts transformer, 750 kVA for local supplies:
RMU and behind 1000 kVA drill tranformer (dry type) 3Ø 1050 Volts:
Name-plate details 600 kVA transformer:
#123025 02/20/06 10:52 AM
I like the puffer breakers that are used.
#123026 02/22/06 02:41 AM
Trumpy Offline OP
By the way Ray,
What does SDAF stand for?.
I've never heard the term before. [Linked Image]
#123027 02/28/06 11:15 AM
Trumpy Offline OP
By the way Ray, regarding the top pic.
Are you guys too cheap (or slack?) to put some DDO's on the pole where the wire heads underground?.
As you know yourself, DDO's aren't just fuses!. [Linked Image]
#123028 02/28/06 03:24 PM
There are fuses in the ring main units, I'm not sure if you use these down south but these ABB units are extensively used in the greater Auckland area.
The first switch of the bank is the isolator.
Second cubilcle is the metering CT's and VT's.
third is switch fuse with 50 Amp fuses.
fourth is switch fuse with 80 Amp fuses.
fifth is switch fuse with 125 Amp fuses.
I haven't seen 200 Amp ddo's and the end of this line is probably unable to supply that load anyway.
[This message has been edited by RODALCO (edited 02-28-2006).]