0 members (),
516
guests, and
17
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jan 2003
Posts: 4,391
OP
Moderator
|
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
VERY NICE!!! Square -D too I like!~!!! Only thing that would raise a bit of concern up here is the black being used and I.D. as "green" and "white".. No big deal though. ( inspectors are finiky here, they have a weird fasination with green and white wire).. I know you don't need them here, and I am not being picky by any means whatsoever , but even when not required I like to throw on a few plastic bushings on the ends of the connectors, just for a bit of added protection and "decoration" (more so the big ones, not so much for the smaller conduits unless its required or spec'd). A.D [This message has been edited by Rewired (edited 01-02-2006).]
|
|
|
|
Joined: Jan 2003
Posts: 4,391
OP
Moderator
|
Thanks. In all three panels the black re-marked white is larger than 6 AWG so unless there is a local amendment it must be accepted per 200.6(B). The EGC in pictures 1 and 2 are also larger than 6 AWG so they must also be accepted per 250.119(A). However the EGC in picture 3 is 8 AWG and is therefore in violation of 250.119. Not much of an excuse other than the customers representative (an electrician himself) supplied the material.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2003
Posts: 4,391
OP
Moderator
|
and I am not being picky by any means whatsoever No! Be picky, rip it up, have fun. I would never post a picture of electric work here and expect people not to be picky. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2005
Posts: 361
Member
|
I offer them here to be dissected to bits by the members here.The panels in pix #1 and #3 aren't plumb...j/k Seriously though, why is the panel in #3 bottom feed from a top feeder? Couldn't the guts just have been flipped? There appears to be more than enough room for bending radii (as there usually is with Square D QOB panels), if that was the issue. EDIT: New year and I still can't spell [This message has been edited by Celtic (edited 01-02-2006).]
~~ CELTIC ~~ ...-= NJ =-...
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Well know we know why they call you hack, diy, wannabe, scab, etc over at the other forum. Nice job.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
OP
Moderator
|
Thanks gentlemen. Seriously though, why is the panel in #3 bottom feed from a top feeder? Good question. Yes the guts can be flipped as where the ones above. The feeder raceway had to come in at the extreme corner. With the feeder on the side I felt going bottom feed was better. The reason is any additional KOs will need to be drilled into the top, by bottom feeding the feeders are nowhere near the 'drilling zone'. This comes from the service guy in me. Normally my preference would be as the top two panels are (center top feed) which also keeps the feeders away from future work. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2006
Posts: 558
Member
|
I also really like how you have all the conduits run down and on Uni-strut!!! like I said before VERY NICE.. Work of art it is! Then again, electrical IS an art is it not?
About that re-colour coding though: thats where Canadian codes and American code differs a bit I guess.. I don't think we are allowed to re-code anything smaller than #2??? Something like that anyway, at least on services. I will have to research that more! Meh, no biggie though , it all works and is SAFE!! A.D
[This message has been edited by Rewired (edited 01-02-2006).]
|
|
|
|
Joined: Jul 2002
Posts: 680
Member
|
You could have spent more time making 90s in the wire where it goes into the breaker .
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
Actually there has been research that shows the conductors are better off not being squared off as they make bends. The sweeps as Bob has installed are a very good job.
Bob You have performed work to make our industry proud. Re-identifying conductors is common practice in our industry.
The only thing I would comment on is the tyrapping of the conductors. I used to do that, but stopped a while ago. Isn't it great to be able to do such good work?
Pierre Belarge
|
|
|
Posts: 75
Joined: June 2012
|
|
|
|