These are in a new commercial kitchen under a peninsular food prep counter. What do you suppose the installer was thinking?Submitted by Lostazhell
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
OK- so he didn't use a 'real' floor box! Let's at least give the guy credit for having his heart in the right place; there is a gasket, the cover will keep stuff from dripping in, and -if all are placed like this one- they are out of the way of foot trafic. Not that I expect the covers to last very long!
Even a rated floor box would allow stuff to drip inside, and surely wouldn't keep mopwater out whereever there was a plug inserted. I think this application would be better served by "tombstone" pedestals for stuff under the counters, and drop cords for everything else.
As nice, reliable, and prooven GFCI's are, they are no substitute for good design.
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
What do I think he was thinking ? He wasn't ! He obviously has never worked in a kitchen when it is washdown time. Alan.
Alan-- If it was easy, anyone could do it.
|
|
|
|
Joined: May 2005
Posts: 247
Member
|
I bet he was thinking "damn architects.. how the ****** am I supposed to do this, and keep the outlets dry when they mop the floor?"
Personally, I would have brought the outlets down from above on pendants, and kept the floor clear.
I don't think that brass floor plates would work well here, A/V style floor pockets would collect water and crud, and the office style speed bumps would probably have the same problem, with no protection. The other option might be to mount a piece of strut, and mount the outlets above the floor level, fed with LT from below.
(edited to remove "misspelled" profanity)
[This message has been edited by electure (edited 06-22-2005).]
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I bet he was thinking "damn architects.. how the #@^% am I supposed to do this, and keep the outlets dry when they mop the floor?" I second that thought. I doubt an electrician decided that spot needed floor outlets. At least they are GFCI.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2004
Posts: 329
Member
|
Personally I would hope that a GFCI CB feeds these outlets. A wash down would most likely drip on the unprotected (line) side of those GFIs. IMHO putting any recepts on the floor in a washdown area like that is like playing Russian Ruelette. Pendants from the ceiling would have been my choice.
|
|
|
|
Joined: Dec 2000
Posts: 4,294
OP
Member
|
In this government building, the floor is liberally sprinkled with receptacles like this one. Cut-in box, device- and cover suspended above it all by the carpet and padding. What was that rule about space between the box and flammable materials? Figure there's a 1/4 inch gap at each one. Oh, and wouldn't you like to be the carpet cleaner? At least, with a receptacle under each cluster of desks, they weren't using extension cords. Renosteinke
|
|
|
|
Joined: Nov 2002
Posts: 794 Likes: 3
Member
|
That government building office wasn't the electrical inspector's, was it?
|
|
|
|
Joined: Feb 2004
Posts: 1,438
Member
|
FYI.... The prints called for cord drops which is what they have now...
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
So Randy, what do the boxes on the floor have now?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|