#120920 05/22/05 02:29 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Quote
Here are two pics showing hazardous-location (classified area) wiring done by someone who wasn't clear on the concept.

The first is of the entrance to a pre-fab, "engineered" booth for painting trucks. While the lights are technically outside the booth, and thus outside the 'zone', one light, as well as the controls are within 3 ft of the door, and thus within the zone (516.3B4)

I am so reassured to know that someone is out there, manufacturing these booths by the hundreds!
[Linked Image]

[Linked Image]
Quote
The second pic shows the disconnect for a propane distributor's pump. Fittings used reveal that EMT was run after the seal, then transitioned near the ground to PVC.

It is permitted to use PVC for the underground portion- but the transition is to be made two feet down, after the bend. EMT after the seal is, of course, not very "explosion- proof" at all

What bothers me most about these pics is that in both cases- one a manufacturer, and the other a utility-type company- there had to have been numerous "professionals" involved who should have known better.

- renosteinke
[Linked Image]

Joined: Mar 2005
Posts: 1,803
Member
From the sprayed writing on the metal wallwork, was this thing built upside down?
Alan


Wood work but can't!
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
No, Alan- but sharp eye! The booth was torn down and transported when the customer moved to a new site!