216
11
Posts: 3,682 Likes: 3
Administrator Member
Doesn't look too bad with the cover on - save for the "temporary" power strip screwed to the wall. Since the insulation is stripped back so far on the breakers, you get a good look at the conductors. The lower wire on the top twin 20 sure looks like it could be aluminum. In a word - UGLY
Whats with the white wire on the twin breaker in the 2nd pic? 240v to the breaker under it? Do they make a handle tie for this 8^) Rod
It looks like a GFCI breaker with no load conductors to me.
Isn't the GFCI wired with the LINE conductors coming into the LOAD terminals?
That might be a problem...
is that 200A panel used as a sub panel? what i mean is, is the 2 aluminum fused some were else in line.
the meter is on the other side of the wall, the 200 amp breaker was the first disconnect