#120783 - 05/04/05 06:16 PM
Re: HVAC T-Stat Wire Routing
|
Member
Registered: 07/05/02
Posts: 8344
Loc: SI,New Zealand
|
John, I used to work for a company here that specialised in installing AirCon/HVAC equipment and the majority of our systems worked off of a Pressure switch. Running a thermostat wire inside the same conduit as the Mains wiring sounds a little dangerous, considering that the T/Stat wire is often very lightly insulated, to say the least. Speaking of insulation, were these pictures taken before the HVAC guy had a chance to insulate his pipe-work?. Often the liquid (smaller) line would go un-insulated here. I was hooking up the power to a new house recently where the Building Inspector refused to sign-off the Building Completion Notice until there was insulation on the Gas (larger) pipe of the AC system. Un-insulated pipes like this cause water problems from dripping Condensation. 
_________________________
Let's face it, these days if you're not young, you're old - Red Green
|
|
Top
|
|
|
|
#120785 - 05/05/05 03:10 AM
Re: HVAC T-Stat Wire Routing
|
Member
Registered: 07/05/02
Posts: 8344
Loc: SI,New Zealand
|
BTW John, Who was that idiot that nailed that dwang (Horizontal timber piece) in to hold the T-stat wire, in the top pic?. Looks like the nail-gun completely missed as did the person fitting the dwang. 
_________________________
Let's face it, these days if you're not young, you're old - Red Green
|
|
Top
|
|
|
|
#120788 - 05/06/05 11:04 AM
Re: HVAC T-Stat Wire Routing
|
Member
Registered: 11/22/03
Posts: 14
Loc: racine, wi
|
Looks like the stud split, on the right, where Mr. HVAC added his 2x4. Just proves anybody can be an electrician if they get hte right matchbook cover!
|
|
Top
|
|
|
|
#201517 - 06/06/11 08:12 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
Here in NJ a lot of HVAC people have EC's working for them. A lic. EC will sign all the permits and hopefully do the electric work.
|
|
Top
|
|
|
|
#201519 - 06/06/11 09:00 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Harold:
Are you tastefully implying something ???
"A lic. EC will sign all the permits and hopefully do the electric"
_________________________
John
|
|
Top
|
|
|
|
#201523 - 06/06/11 10:59 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 10/25/06
Posts: 713
Loc: Springfield, VA, USA
|
I know that this is sort of unrelated, but I am curious to know what the heck that gas stub-out is for. It doesn't make much sense to me unless I'm missing something.
_________________________
---Ed---
"But the guy at Home Depot said it would work."
|
|
Top
|
|
|
|
#201528 - 06/06/11 12:55 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Ed:
Although I did not take the pics within, this is a common rough out for a warm air furnace with an 'A' coil for the AC. Gas is for the heating portion.
_________________________
John
|
|
Top
|
|
|
|
#201529 - 06/06/11 01:40 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 10/25/06
Posts: 713
Loc: Springfield, VA, USA
|
I thought that as well, John. I guess what had me stumped was the block of wood that appeared to have been placed for a thermostat. In all my days, I've never seen a thermostat located so closely to a furnace.
_________________________
---Ed---
"But the guy at Home Depot said it would work."
|
|
Top
|
|
|
|
#201530 - 06/06/11 03:13 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
I guess the HVAC guy wanted the t'stat wire right there for some reason.
_________________________
John
|
|
Top
|
|
|
|
#201881 - 06/29/11 09:41 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 03/23/05
Posts: 1757
Loc: Mayenne N. France
|
tshea is right. Blown up, you can see the stud was split. How else would a framing nailer get the heads flush with the stud? 'Someone' then worked over the area with an electric [?] planer to smoothe it over, hence the shavings on the deck. When sheetrocked, there will be a huge shallow dent.
_________________________
Wood work but won't!
|
|
Top
|
|
|
|
#201943 - 07/05/11 09:57 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 07/20/04
Posts: 7143
Loc: Estero,Fl,usa
|
I know I am late on this but I always see the T stat wire run with the freon line set. The installer tapes the T-stat wire to the outside of the armaflex while he is putting it on the evaporator line. Then they run it all together as an assembly. That also eliminates the problem of the electrical inspector complaining about it being taped to the seal tight.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#201954 - 07/06/11 12:52 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Tape is not an approved means of support for any cabling! Comments?
_________________________
John
|
|
Top
|
|
|
|
#201960 - 07/06/11 04:37 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 07/20/04
Posts: 7143
Loc: Estero,Fl,usa
|
Cite that. I don't see any listing mark on tywraps or Romex staples either. 
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#202106 - 07/18/11 07:34 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
John,
Yes, I guess you could say I was tastefully stating the fact that all permits signed by an EC, might not ever see a Lic. EC on site. After seeing some of the work done, you just KNOW an EC wasn't there.
|
|
Top
|
|
|
|
#202107 - 07/18/11 07:37 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
Greg, What about that all important sec of the code? 90.4 which says, you do as I say? A lot of AHJ's hide behind that section a lot.
|
|
Top
|
|
|
|
#202117 - 07/18/11 12:18 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Harold;
Yes, you were tasteful! I refer to those guys as "paper hangers"!
Amazing, when the EC is called/contactedfor a violation, the responses are really funny. "What job"; "what are you talking about"; "never heard of that person"....etc.
It's even hilarious when no corrections are made, and the EC of record shows up at the counter with the Notice of Violation & monetary penalty in hand!!
_________________________
John
|
|
Top
|
|
|
|
#202124 - 07/18/11 10:25 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 07/20/04
Posts: 7143
Loc: Estero,Fl,usa
|
I doubt most electrical inspectors have ever seen an installed A/C condenser on a job site. The EC sets the disconnect, gets his final and that is it. The condenser might drop the day before the customer closes. (along with the appliances)
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#202125 - 07/19/11 07:27 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Greg: Up here, a 'Final' inspection means just that "Final". All equipment must be installed.
There is no way that I am aware of to check the circuit for the compressor without seeing the nameplate, for minimum circuit ampacity, and max OCP.
Harold & I are talking about replacement HVAC. A Lic EC is required for the compressor up here.
_________________________
John
|
|
Top
|
|
|
|
#202126 - 07/19/11 12:40 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 07/20/04
Posts: 7143
Loc: Estero,Fl,usa
|
Florida will allow the HVAC contractor to make up the whip to the disconnect. They usually will not drop the condenser until the last minute because they have a habit of walking away. The flip side of that is that the disconnect will usually be wired to 310.16 so it really doesn't matter that much how big the condenser is since the wire is plenty big.
_________________________
Greg Fretwell
|
|
Top
|
|
|
|
#202133 - 07/20/11 07:34 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
Greg,
As John said, on new houses or new HVAC jobs, the outside compressor has to be installed. If the HO wants to move in before the outside unit is ready, my boss will allow them to Co the building, but they have to pull a new permit for the units that weren't installed. This way we can get back into the building to check the HVAC when they are installed.
|
|
Top
|
|
|
|
#202134 - 07/20/11 07:40 AM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 02/16/02
Posts: 1823
Loc: Boonton, NJ
|
John,
Just today I see a permit on my desk. It was for an HVAC replacement. I did plan review on 6/24 and noticed that the permit for electric wasn't sealed and was filled in by the HVAC contractor. I called him up and left a message stating that the permit needed to be signed and sealed. So today as I walk into the office, the permit was on my desk. I thought the permit might have been sealed, but to my surprise, I saw a copy of a bill in here that the job was already done and paid for. The best part of this whole story is that the bil was dated 5/24/11. That was almost a month before we even got the permit for plan review. I can't wait to here the story behind this one.
|
|
Top
|
|
|
|
#202142 - 07/20/11 02:00 PM
Re: HVAC T-Stat Wire Routing
[Re: Webmaster]
|
Member
Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
|
Harold: Before Bill has us arrested for 'jacking' this thread, perhaps either you or I can start a thread on the permitting issues!
Quickly, yuor situation above, I would send the HVAC guy a Notice of Violation, Electrical Subcode & Administrative, for $1000 to get his attention!
edit: I started a thread for permit issues for AHJs and ECs. Lets carry this on there, OK?
Edited by HotLine1 (07/20/11 02:12 PM)
_________________________
John
|
|