by ale348 - 03/29/24 01:09 AM
by NORCAL - 03/19/24 05:11 PM
#119865 02/05/05 04:47 PM
Would this pass 230.70 A (1) "The service disconnecting means shall be installed at a readily accessible location either outside of a building or nearest the point of entrance of service conductors." The cable continues three feet outside the picture and out to the meter.
Electricmanscott
#119866 02/05/05 05:50 PM
Electricmanscott, I would say you are right at the limit of Mass Electric Code 230.70 A (1) which allows you to go 10'. Under the NEC I would say this would not pass.
Al
#119867 02/05/05 06:09 PM
Al that section requires the disconnect if located outside to be within 10' of building served.
Inside it is still 'nearest the point of entrance'.
As you know I have not done many home services but I thought most of the inspectors are looking for 5' or less?
2002 Mass amendments
230.70(A)(1). Revise to read as
follows:
(1) Readily Accessible Location. The service
disconnecting means shall be installed at a readily accessible location either outside and attached to or within 3 m (10 ft) of the building or structure served, or inside nearest the point of entrance of the service conductors.
In my opinion the wording is tough to decipher.
I have not seen the 2005 amendments, perhaps there is a change.
Bob
#119868 02/05/05 06:19 PM
Bob, still reads the same for '05. By the way I did not, and would not install this.
[This message has been edited by Electricmanscott (edited 02-05-2005).]
#119869 02/05/05 06:27 PM
Scott
He** I knew that. [Linked Image]
Bob
#119870 02/05/05 09:35 PM
NO...that is beyond the nearest point IMO.
shortcircuit
#119871 02/07/05 06:29 PM
Not a chance on God's green earth (around here)
#119872 02/07/05 06:57 PM
Scott
Is the masonary wall clear of obstruction and provides access per 110.26??
No Oil Tanks Etc.Just curious!!
Charlie
#119873 02/07/05 07:00 PM
Wouldn't pass here. [Linked Image]
Ryan Jackson,
Salt Lake City
#119874 02/07/05 07:56 PM
V
NM stapled on the face of those 2x4's wouldn't pass around here either
