210
12
Posts: 3,682 Likes: 3
Administrator Member
shortcircuit, nice job. Great picture of the proper use of SEU cable. If that was an FPE panel it sure lived up to its name Fire Prone Equipment.
Al
Posts: 943 Likes: 2
From the look of the panel trim I would guess it is a Crouse-Hinds/ Murray panel.Good thing no one was hurt.
Thank you! That cable looks fine. How's the service drop attached?
So that is how to modify a panel cover to accept more OCPDs. Pierre
Pierre Belarge
Service drop is attached to the left of the weatherhead to a porcelin insulator anchored to the corner of the house.
I also like using the handy straps on the SEU which nail to the wood siding.With one screw in the weatherhead,the whole assembly will release from the building when a branch from the trees in the yard hit the drop during storms without alot of damage to the cable or building.Sometimes we can just clip the SEU right back to the house.
I also will fill the PVC weatherhead with silicone,duct seal the wet connector at the top of the meter can,duct seal the cable inside the meter where it exits the bottom of the meter,and silicone and duct seal where the the SEU penetrates the building. Also punch out the drain hole at bottom of meter and use water stop butt connectors at point of connection to the utility drop...which is the electricians responsibility to make up (live) on service changes and repairs in this area.
shortcircuit
Hi, Just wondering what protection you have on that se cable between the meterbase and the panel? If there is no breaker or fuse between them, then the se cable requires protection does'nt it?
-Regards
Greg
Not IIRC.
My wife's grandmother's house isn't rigged that way, and neither are any of her heighbors (my only exposure to SEU)
IMO...the SE installed in the pictures is NOT exposed to physical damage.The cable is supported according to 230.51(A).
I don't know of any code that requires extra protection of the SE cable between the meter socket and the service disconnect.
Also take note of compliance with 230.70(A)(1)the service disconnecting means is located inside NEAREST the point of entrance of the service entrance conductors.
shortcircuit
With one screw in the weatherhead,the whole assembly will release from the building Is this desireable? Are they all done this way?
