#11941 07/27/02 11:14 AM
aldav53 Offline OP
In a 3 Phase service I have seen 240v between phases and a 208 to ground wild leg, What are some other combinations and where do they use the wild leg?
#11942 07/27/02 12:26 PM
Search for high leg (27 hits) or 4-wire delta (4 hits) at this site.
Note that “Bø” {or sometimes Cø} can also be called Stinger / Red / Orange / Purple / Power / Wild / Bastard / High Leg
Read through Scott35’s 3 Phase Delta Transformer Schematics in Technical Reference Area of this board.
Also see: home.att.net/~benmiller/elecsys.htm
Utility availability of this service type is usually limited to small, remote overhead systems.
Other non-symmetrical 3ø configurations are the corner-grounded variety.
[This message has been edited by Bjarney (edited 07-27-2002).]
#11943 08/02/02 11:26 AM
aldav53 Offline OP
I was unable to find any data in the technical Reference area.
#11944 08/02/02 12:38 PM
Al,
Did you set the selection to see all topics?
We are working on a way to have them continuously visible regardless of date, but this works for now. Look at the thread in that area for Instructions if you're not sure what I mean.
#11945 08/02/02 07:08 PM
aldav53 Offline OP
Yep, I tried that, no subjects come up.
#11946 08/02/02 07:22 PM
Alda,
The wild leg is ONLY useful in configurations that do not require a neutral, such as 3 phase equipment, or 240 volt loads with no neutral, otherwise you burn it up.
You ONLY have a high leg in Delta systems (open or closed) because you tap mid phase of one coil (between A and C)
That's why the Wye is the popular form today, it creates no high leg and all 3 phases are useful with the neutral.
You often see 199 volt high legs, this is from 230 volt systems. Phase to ground voltage of A or C phase X 1.732 = phase to B voltage.
#11947 08/02/02 07:57 PM
Al,
Take a look to see if this is what you are looking for.
https://www.electrical-contractor.net/ubb/Forum15/HTML/000054.html
#11948 08/02/02 08:49 PM
'Wild leg' is no longer the term i like.
Has you ever yelled out
got the WILD LEG'
in a crowded store or mall???
[This message has been edited by sparky (edited 08-02-2002).]
#11949 08/04/02 03:22 AM
aldav53 Offline OP
Thanks for the answers, Bill great transformer drawings, but still not sure where they are used. On a 3ph system 240v between phases and measuring "120v to grd, 120v to gnd, and 208 to gnd", where would the 208v to gnd be used?
#11950 08/04/02 08:20 AM
Aldav53,
The high leg (208 to ground) exists as a result of the center tap, but is not used to supply loads.
Ed