just a dumb little question, ive seen this in a few boxs where they will use one neutral per three circurts, I myself like to give each circurt its own neutral. is this becoming or has been a way to save money. just wondering is all thanks joe
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Joe, I'm going to assume you are new into the trade. Please research branch circuit multiwire covered in the NEC Article 100. as well as 300 and 310 and more.
I don't mean to leave you hanging, but if you read these articles it will help more than an answer on the internet.
Remember that a grounded conductor per one circuit is not a neutral in reality.
Roger
|
|
|
|
Joined: Jul 2002
Posts: 6
OP
Junior Member
|
roger, thanks and youre not leaving me hanging there at all. ill take the time to check it out. Joe
|
|
|
|
Joined: Jan 2002
Posts: 163
Member
|
Joe -
You asked if 'this' was a way of saving money....I'm sure that may play some part with this practice, but if you check out 310-15(b)(4)(a) [1999] this will give a good reason for using the shared neutral. Example: if you tried to pull 6 circuits in a conduit using your one-neutral-per-circuit method you would have to derate the conductors 50% (Table 310-15b2a)... #12 THHN would only be rated for a 15A circuit ... using the shared neutral process you only derate 20%....in fact, you could get nine 20A circuits (using #12THHN) in one conduit (shared neutral method)vs. only 4 circuits using your method....god I hope I didn't blow my arithmetic!
|
|
|
|
Joined: Jul 2002
Posts: 6
OP
Junior Member
|
Dana, that clears it up for me and i do see your point. Joe
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
lynnbar,
You have to realize that this is only an option under certain circumstances, it cannot always be done. For what you describe it would have to be a Three-Phase system and all on different 'phases' or 'legs'.
Bill
Bill
|
|
|
|
Joined: Jul 2002
Posts: 6
OP
Junior Member
|
bill, thats where i seen this at on a 3 phase panel, joe
|
|
|