ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Quote
These were found on a recent job site i was out on to install smoke detectors thru out (good thing!!!!);

a pictue of a service in a row home basement in south jersey. Can you count the violations? The other picture is of the hot water heater in the same job,(the pictue doesn't do it justice the span on that romex is about 4 feet, the other pic is above the drop ceiling in the kitchen open jb's and gotta love that ceiling fan & flying splice support.enjoy

- NJ Wireman
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Joined: Nov 2001
Posts: 745
M
Member
Wireman: I'm surprised the sewer line and telephone equipment aren't crammed into this same little corner [Linked Image].

On a hot summer day, I guess the EC could set the washing machine to cold water and dangle his feet inside it while he works on the panel [Linked Image].

Incredibly bad mix of utilities and working spaces (or lack thereof).

Mike (mamills)

BTW: What is that black looking thing hanging down from the joists, just above that little sub-panel?

[This message has been edited by mamills (edited 09-13-2004).]

Joined: May 2002
Posts: 110
M
Member
OK...I'm going to take a stab at this. I can't quote the NEC reference.
#1. Inadequate working clearance in front of equipment likely to be serviced.
#2. 1 laundry recepticle is required and does not need to be GFCI protected. The second duplex needs GFCI protection. If it is protected by a GFCI breaker then it needs to have the yellow tag stating such.
#3. Water pipes occupying the area directly above the service panel.
#4. No bonding jumper at the water meter.
#5 Panel on the side has wires that are not protected.
#6 Inadequate conductor size for the water heater. No protection also. It looks like 14 gage NM cable.
#7. Flying splices in the drop ceiling.
#8. No covers on the boxes.
#9. Too many conductors in the romex connector at the jbox.
#10. Cover screw missing from the loadcenter.

#11. Nutdriver left on the washing machine.(OK, Just kidding)

Wow, now i'm tired.

Blessings and GOD Bless America
Mark Randazzo

Joined: Feb 2002
Posts: 114
E
Member
Without rotating the water heater so that the power is closer to the wall - how would you properly support the NM? (I'm a telecom guy, not an electrician, so forgive my ignorance if the answer is pretty obvious)

What is holding up the gas meter? That is a gas meter, right?

Joined: May 2002
Posts: 110
M
Member
I believe you would consider it a fixture whip. I would not need to be supported for that short distance. But it has to be protected. i.e. a raceway sleeve.

Blessings and GOD Bless America
Mark Randazzo

Joined: Oct 2004
Posts: 17
W
Member
My, oh my! Gas and electric so close together. At least if there's a fire, the water will put it out!
:-)>

James

Joined: Aug 2003
Posts: 1,374
R
Moderator
Ah...I've been looking for my nut driver...there it is. I'll have to go back there and grab it.

Thanks!