0 members (),
220
guests, and
12
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 3,682 Likes: 3
OP
Administrator Member
|
Is this a Violation?
- Ron
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
I'll hazard a guess that it could be if the connectors were used as a required disconnect for whatever machinery is running on them, as the plugs would not be quickly and easily withdrawable.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
I was thinking the same thing Paul.
Bill
Bill
|
|
|
|
Joined: Apr 2002
Posts: 7,381 Likes: 7
Member
|
As above, if the caps are the disco, yes, a red sticker.
Also, is this a use of cord that is not compliant with Art 400.7 / 400.8 limitations to usage of cord? As the install is not completly visable, no determination can be made.
If pull out is a problem, the installer should have considered twistlock devices, in lieu of ty-wraps.
John
John
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Also, the sealtite flex doesn't appear to be secured within 12" of the boxes, so yes. 350.30(A) We're also looking at 225° (at least) of bend just to get out of the center box. Could it possibly exceed 360° between pull points? 350.26
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Generally we use twist locks. This looks to me like a under a data room floor. If it is under 645 rules the liquid-tight need not be secured, the same for the box. 645.6(E) We do a lot of installs where the UPS maker supplies pre-made liquid-tight whips with FS type boxes and receptacles. For better or worse all you do is drop them in like extension cords. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
The 3/4" square tube legs that are bonded with the bare copper along with what looks like a piece of fiberoptic cable in the bottom of the picture are what makes me think this is a 645 room.
Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Mar 2002
Posts: 582
Member
|
Sorry to be away for so much activity. It is an Article 645 installation. The plugs are for computer servers, not requiring a means of disconnect like a motor.
Ron
|
|
|
|
Joined: Mar 2002
Posts: 582
Member
|
The server cords do not have twist lock plugs, hence the straight blade receptacle. No one wants to cut the factory plug off a server.
Ron
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Bob, Don't you mean 645.5(E)??
Now read 645.5(D)(2) "installed in accordance with 310.11" These don't look like a specially listed whip to me.
|
|
|
Posts: 43
Joined: September 2013
|
|
|
|