1 members (Scott35), 216 guests, and 11 robots.
#117795 07/09/04 12:01 PM
Is this a Violation?
- Ron
#117796 07/09/04 03:21 PM
I'll hazard a guess that it could be if the connectors were used as a required disconnect for whatever machinery is running on them, as the plugs would not be quickly and easily withdrawable.
#117797 07/09/04 03:24 PM
I was thinking the same thing Paul.
#117798 07/09/04 03:36 PM
As above, if the caps are the disco, yes, a red sticker.
Also, is this a use of cord that is not compliant with Art 400.7 / 400.8 limitations to usage of cord? As the install is not completly visable, no determination can be made.
If pull out is a problem, the installer should have considered twistlock devices, in lieu of ty-wraps.
#117799 07/09/04 05:44 PM
Also, the sealtite flex doesn't appear to be secured within 12" of the boxes, so yes.
350.30(A)
We're also looking at 225° (at least) of bend just to get out of the center box. Could it possibly exceed 360° between pull points?
350.26
#117800 07/09/04 06:01 PM
Generally we use twist locks. [Linked Image]
This looks to me like a under a data room floor.
If it is under 645 rules the liquid-tight need not be secured, the same for the box. 645.6(E)
We do a lot of installs where the UPS maker supplies pre-made liquid-tight whips with FS type boxes and receptacles.
For better or worse all you do is drop them in like extension cords.
Bob
#117801 07/09/04 06:05 PM
The 3/4" square tube legs that are bonded with the bare copper along with what looks like a piece of fiberoptic cable in the bottom of the picture are what makes me think this is a 645 room.
Bob
#117802 07/09/04 06:20 PM
Ron Offline
Sorry to be away for so much activity.
It is an Article 645 installation. The plugs are for computer servers, not requiring a means of disconnect like a motor.
Ron
#117803 07/09/04 06:22 PM
Ron Offline
The server cords do not have twist lock plugs, hence the straight blade receptacle. No one wants to cut the factory plug off a server.
Ron
#117804 07/09/04 09:53 PM
Bob,
Don't you mean 645.5(E)??
Now read 645.5(D)(2)
"installed in accordance with 310.11"
These don't look like a specially listed whip to me.
