2 members (Scott35, HotLine1), 238 guests, and 26 robots.
#117042 05/16/04 09:54 PM
I found this in a friends house a three way lamp was plugged into it. It works and is wired right But this is probably a violation.
- Peter
#117043 05/17/04 01:06 PM
404.14(E) Dimmer Switches. General-use dimmer switches shall be used only to control permanently installed incandescent luminaires (lighting fixtures) unless listed for the control of other loads and installed accordingly.
#117044 05/17/04 08:09 PM
This probably has a plug on the other end of the zip cord. In that case, does NEC apply?
/mike
#117045 05/18/04 09:35 AM
Hi I'm Peter,
Yes it does have a plug on the other end.
Theres always enough room in the junction box.You just need a bigger hammer
#117046 05/18/04 02:58 PM
I don't understand, why not get one of those plug-in table top dimmers where you plug it into the wall, plug the lamp into the through-tap and there's a cord with a dimmer switch at the end?
Alternatively, you can get a dimmer switch that attaches to the lamp's cord like a regular on-cord switch, except that instead of a rocker, it has a knob that you turn with your thumb.
Either of the above solutions would have been simpler, cheaper and safer than this kludge that Peter shows us. [Linked Image]
EDIT: Also, those boxes are not listed for that type of portable application. The metal ones have knockouts that can break off and the plastic boxes will shatter like a phonograph record if dropped on the floor, kicked or banged.
[This message has been edited by SvenNYC (edited 05-18-2004).]
#117047 05/18/04 06:18 PM
I definitely agree with the issues concerning durability, and I don't like the idea of this thing getting knocked around by that piece of zip-cord with no gromets or strain-relief to speak of.
But on the plus side, at least they had sense enough not to use a grounding-type receptacle and what appears to be heavier-than-normal 16 gauge lamp cord...
It's pretty bad when I look at something like this and think: "Well, it could be worse...." [Linked Image]
-John
#117048 05/22/04 08:18 PM
that looks like a new ungrounded receptacle... why would they still make these? [Linked Image]
#117049 05/22/04 08:35 PM
Matt,
Ungrounded receptacles are still made for situations where there is an existing ungrounded receptacle needing replacement. Instead of replacing the receptacle with a GFCI, you can use one of these. However... they are sold at "home centers" and the last time I looked, El Cheapo outlets from the big bin were about 40ยข, while these cost over $1.50. It's likely that the NEMA 5-15 outlets are used with nothing connected to the ground, instead of using these 1-15's
Edited because im in YIM mode and abbreviate everything
[This message has been edited by sparked (edited 05-22-2004).]
#117050 05/23/04 01:47 AM
ah i c... makes sense to me [Linked Image]... i've just never seen these before in any hardware stores.
[This message has been edited by MattE (edited 05-23-2004).]
