this is a two and one half gal comp conn. is it listed for outdoor, for say use as a conn in a meter hub?
- richard
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2004
Posts: 79
Member
|
If the price of steel goes up anymore, you may want to buy a nice chain and hang it around your neck instead.
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
|
|
|
|
Joined: Jun 2001
Posts: 642
Member
|
Check the manufacturers box label to see if it listed for a wet location. If it is not then you cannot use it outside.
ed
|
|
|
|
Joined: Apr 2001
Posts: 518
Member
|
The controversy is new; untill UL questioned its' classifications, they were. Under the new criteria, only EMT fittings to 1" have so far been listed. I'm not even sure if the controversy extended to anything but EMT fittings. Logic might say 'yes,' but the UL statements were pretty specific in singling out EMT fittings.
As to your question: Generally, yes. The exception is when used on the top surface of a box, panel, etc. In that situation, it is necessary to use a Myers' hub. If, as is the case with most service equipment, you are connecting to a raised hub, they're fine. (The concern is that pooled water will seep in at the point where the fitting meets the sheet metal. A Myers' hub has a gasketed face.)
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
John, Did you find any listed as raintight?
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
I’m out of the loop these days, but in the 1980-1990 decades, in 2½-4-inch size, the only listed raintite fittings were made by “ETP Berger” and they were a compression-gland type connector/coupling with a very visible black-rubber boot as part of the gland nut. At that time, all other 2½-4-inch compression fittings were listed concrete-tite, but not raintite. ETP now seems to be part of OZ-Gedney, and I can’t find this type of fitting in their online catalog. Does anyone remember these? ETP even made raceway and elbows with integral 2½-4-inch booted-raintite couplings swaged on one end.
Note that 2½-4-inch EMT and rigid-metal conduit have the same outside diameters, but threadless fittings for either are not intended {or listed} to be interchangeable.
|
|
|