#115620 - 11/20/03 05:51 AM
Pancakes, Anyone?
|
Moderator
Member
Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
|
This box is a (Hubbell) Raco 3.5" "Ceiling Box". They've been around since the days of knob & tube wiring. Where would you use this particular box??...S [This message has been edited by electure (edited 11-20-2003).]
|
|
Top
|
|
|
|
#115621 - 11/20/03 07:07 AM
Re: Pancakes, Anyone?
|
Member
Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
|
|
|
Top
|
|
|
|
#115622 - 11/20/03 02:26 PM
Re: Pancakes, Anyone?
|
Member
Registered: 12/11/02
Posts: 25
Loc: Los Angeles, CA, USA
|
Only on a ceiling fixture or wall sconce with a canopy that meets the wire fill requirements.
[This message has been edited by Gus1999 (edited 11-20-2003).]
|
|
Top
|
|
|
|
#115623 - 11/20/03 03:39 PM
Re: Pancakes, Anyone?
|
Member
Registered: 09/23/03
Posts: 101
Loc: Raleigh
|
Well, it's 4.0 cu in-so it's perfect for old fashioned 14-2 Romex with no ground.
|
|
Top
|
|
|
|
#115625 - 11/20/03 06:15 PM
Re: Pancakes, Anyone?
|
Member
Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
|
Now, what about the ground wire in the 14-2 romex?? It doesn't count? Not if you cut it off before it enters the box...who needs a ground for a light fixture anyway? (NOTE: That was supposed to be sarcasam...)
|
|
Top
|
|
|
|
#115626 - 11/20/03 06:57 PM
Re: Pancakes, Anyone?
|
Member
Registered: 09/23/03
Posts: 101
Loc: Raleigh
|
These things always seem to get added onto over time
"You know, I always wanted an outlet there...."
|
|
Top
|
|
|
|
#115628 - 11/20/03 07:08 PM
Re: Pancakes, Anyone?
|
Member
Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
|
I never use the 3.5" ones and never with clamps.
Ceiling fixture that lands on a joist and sconces that land on a stud. They are some of the best support for heavier fixtures since the mounting point is centered on the box.
_________________________
Speedy Petey
"Anyone who has never made a mistake has never tried anything new." -Albert Einstein
|
|
Top
|
|
|
|
#115630 - 11/23/03 08:22 PM
Re: Pancakes, Anyone?
|
Member
Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
|
Bill I respectfully disagree with the your interpretation of the canopies/domes. 370-16(a) permits using the volume of the canopy/dome. I believe the exception you are referencing is to allow for those fixture wires not to be counted as part of box fill.
Pierre
_________________________
Pierre Belarge
|
|
Top
|
|
|
|
#115632 - 11/24/03 05:19 AM
Re: Pancakes, Anyone?
|
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
|
This came up before. I have also never seen a canopy with a volume indicated ? However, wouldn't the volume be based on a (pancake) box with a blank cover installed?
|
|
Top
|
|
|
|
#115633 - 11/24/03 07:43 AM
Re: Pancakes, Anyone?
|
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
|
The ones that I usually see are used in residential and are non metallic (without the clamps).
With that in mind, how do you view it as an inspector? What do you allow or not allow? I will permit (1) 14-2 cable and no more at the rough stage. My reasoning is that I see very few lights with the volume marked on the canopy, and I don't want people having to change out their expensive lights because the rough doesn't comply. Any thoughts on this?
_________________________
Ryan Jackson, Salt Lake City
|
|
Top
|
|
|
|
#115634 - 11/24/03 09:42 AM
Re: Pancakes, Anyone?
|
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
|
Ryan,
Would you flag a 14/3 NM installation to a pancake for a ceiling fan?
This is commonly installed around here.
|
|
Top
|
|
|
|
#115635 - 11/24/03 09:49 AM
Re: Pancakes, Anyone?
|
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
|
Yes I would, unless the installer could show me that the fan has a volume allowance in the canopy. Otherwise I would ask for a "4-O" box instead of a "3-O" box.
_________________________
Ryan Jackson, Salt Lake City
|
|
Top
|
|
|
|
#115636 - 11/24/03 10:32 AM
Re: Pancakes, Anyone?
|
Member
Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
|
Are "pancakes" rated for a ceiling fan (50 lbs, off the top of my head)?
|
|
Top
|
|
|
|
#115637 - 11/25/03 05:33 AM
Re: Pancakes, Anyone?
|
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
|
Thinkgood,
There are specific pancakes designed for fans and heavier fixtures.
|
|
Top
|
|
|
|
#115638 - 11/25/03 06:04 AM
Re: Pancakes, Anyone?
|
Moderator
Member
Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
|
|
|
Top
|
|
|
|
#115639 - 11/25/03 05:04 PM
Re: Pancakes, Anyone?
|
Member
Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
|
The problem with these things is that they are often installed so that they are not flush with the wall surface. Has anyone ever seen extension rings for them?
|
|
Top
|
|
|
|
#115640 - 11/28/03 03:31 PM
Re: Pancakes, Anyone?
|
Member
Registered: 02/17/02
Posts: 55
Loc: los angeles
|
|
|
Top
|
|
|
|
#115641 - 11/29/03 07:13 PM
Re: Pancakes, Anyone?
|
Moderator
Member
Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
|
Arlington's got kind of a unique box for use when the joist's right in the way. (They're a pretty innovative bunch). www.aifittings.com/n_1.htm Anybody tried them?..S [This message has been edited by electure (edited 11-29-2003).]
|
|
Top
|
|
|
|
#115642 - 11/29/03 08:05 PM
Re: Pancakes, Anyone?
|
Member
Registered: 03/08/03
Posts: 10
|
Yes Ive used those "saddle" boxes before, they work rather well.
|
|
Top
|
|
|
|
|
|