#115620 - 11/20/03 05:51 AM Pancakes, Anyone?
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
This box is a (Hubbell) Raco 3.5" "Ceiling Box".
They've been around since the days of knob & tube wiring.



Where would you use this particular box??...S



[This message has been edited by electure (edited 11-20-2003).]

Top
#115621 - 11/20/03 07:07 AM Re: Pancakes, Anyone?
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
See question #11: http://www.electrical-contractor.net/Education/Mike_Holt_Code_Q&A.htm

Substitute 314.16 for 370-16

Top
#115622 - 11/20/03 02:26 PM Re: Pancakes, Anyone?
Gus1999 Offline
Member

Registered: 12/11/02
Posts: 25
Loc: Los Angeles, CA, USA
Only on a ceiling fixture or wall sconce with a canopy that meets the wire fill requirements.

[This message has been edited by Gus1999 (edited 11-20-2003).]

Top
#115623 - 11/20/03 03:39 PM Re: Pancakes, Anyone?
sparked Offline
Member

Registered: 09/23/03
Posts: 101
Loc: Raleigh
Well, it's 4.0 cu in-so it's perfect for old fashioned 14-2 Romex with no ground.

Top
#115624 - 11/20/03 05:06 PM Re: Pancakes, Anyone?
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
I've seen lots of these above sinks in bathrooms on residential work.
Seems that darn plumber always vents straight up, and there's almost always a stud right there...S
TG, yes when they enter from a domed fixture.
Now, what about the ground wire in the 14-2 romex?? It doesn't count?



[This message has been edited by electure (edited 11-20-2003).]

Top
#115625 - 11/20/03 06:15 PM Re: Pancakes, Anyone?
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
 Quote:
Now, what about the ground wire in the 14-2 romex?? It doesn't count?


Not if you cut it off before it enters the box...who needs a ground for a light fixture anyway?

(NOTE: That was supposed to be sarcasam...)

Top
#115626 - 11/20/03 06:57 PM Re: Pancakes, Anyone?
sparked Offline
Member

Registered: 09/23/03
Posts: 101
Loc: Raleigh
These things always seem to get added onto over time

"You know, I always wanted an outlet there...."

Top
#115627 - 11/20/03 07:03 PM Re: Pancakes, Anyone?
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
Now, let's deduct 1 conductor for the clamps
...S

Top
#115628 - 11/20/03 07:08 PM Re: Pancakes, Anyone?
Speedy Petey Offline
Member

Registered: 08/29/03
Posts: 175
Loc: Upstate, NY
I never use the 3.5" ones and never with clamps.

Ceiling fixture that lands on a joist and sconces that land on a stud.
They are some of the best support for heavier fixtures since the mounting point is centered on the box.
_________________________
Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Top
#115629 - 11/22/03 12:48 PM Re: Pancakes, Anyone?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
I've used these before, and reasoned that the Fixture Dome effectively adds volume to the box that can be divided up for conductor fill. It has been a solution for some tough situations.

But ... strictly speaking, 370-16(B)(1)Exception seems to say that the 'domed luminaire' or canopy space can only be used to avoid counting the fixture wires.

Bill

Top
#115630 - 11/23/03 08:22 PM Re: Pancakes, Anyone?
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Bill
I respectfully disagree with the your interpretation of the canopies/domes.
370-16(a) permits using the volume of the canopy/dome. I believe the exception you are referencing is to allow for those fixture wires not to be counted as part of box fill.

Pierre
_________________________
Pierre Belarge

Top
#115631 - 11/23/03 08:37 PM Re: Pancakes, Anyone?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
Pierre,

370-16(A) (and 314.16(A)) talks about "domed covers, extension rings, etc that are marked with their volume in cubic inches..".

I've never seen a fixture canopy that had its volume marked in cubic inches. If this is a 4 cu. in box what code section allows 3 #14s to be in it?

Bill

Top
#115632 - 11/24/03 05:19 AM Re: Pancakes, Anyone?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
This came up before. I have also never seen a canopy with a volume indicated ?
However, wouldn't the volume be based on a (pancake) box with a blank cover installed?

Top
#115633 - 11/24/03 07:43 AM Re: Pancakes, Anyone?
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
The ones that I usually see are used in residential and are non metallic (without the clamps).

With that in mind, how do you view it as an inspector? What do you allow or not allow? I will permit (1) 14-2 cable and no more at the rough stage. My reasoning is that I see very few lights with the volume marked on the canopy, and I don't want people having to change out their expensive lights because the rough doesn't comply. Any thoughts on this?
_________________________
Ryan Jackson,
Salt Lake City

Top
#115634 - 11/24/03 09:42 AM Re: Pancakes, Anyone?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Ryan,

Would you flag a 14/3 NM installation to a pancake for a ceiling fan?

This is commonly installed around here.

Top
#115635 - 11/24/03 09:49 AM Re: Pancakes, Anyone?
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Yes I would, unless the installer could show me that the fan has a volume allowance in the canopy. Otherwise I would ask for a "4-O" box instead of a "3-O" box.
_________________________
Ryan Jackson,
Salt Lake City

Top
#115636 - 11/24/03 10:32 AM Re: Pancakes, Anyone?
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
Are "pancakes" rated for a ceiling fan (50 lbs, off the top of my head)?

Top
#115637 - 11/25/03 05:33 AM Re: Pancakes, Anyone?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Thinkgood,

There are specific pancakes designed for fans and heavier fixtures.

Top
#115638 - 11/25/03 06:04 AM Re: Pancakes, Anyone?
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA

Top
#115639 - 11/25/03 05:04 PM Re: Pancakes, Anyone?
John Steinke Offline
Member

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
The problem with these things is that they are often installed so that they are not flush with the wall surface.
Has anyone ever seen extension rings for them?

Top
#115640 - 11/28/03 03:31 PM Re: Pancakes, Anyone?
drgnz23 Offline
Member

Registered: 02/17/02
Posts: 55
Loc: los angeles
to install ceiling fans

Top
#115641 - 11/29/03 07:13 PM Re: Pancakes, Anyone?
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
Arlington's got kind of a unique box for use when the joist's right in the way. (They're a pretty innovative bunch).
www.aifittings.com/n_1.htm
Anybody tried them?..S

[This message has been edited by electure (edited 11-29-2003).]

Top
#115642 - 11/29/03 08:05 PM Re: Pancakes, Anyone?
Tim Peters Offline
Member

Registered: 03/08/03
Posts: 10
Yes Ive used those "saddle" boxes before, they work rather well.

Top