#115404 10/24/03 11:48 PM
Is it a violation for a water pipe to be under the equipment here?
Joe
#115405 10/25/03 11:49 AM
While there is not a violation of the safety work space required by 110.26(A), there is a violation of the "dedicated equipment space" required by 110.25(F)(1)(a).
Don
#115406 10/25/03 04:31 PM
I am wondering about what looks like the use of parallel conductors smaller than 1/0?
Bob
#115407 10/25/03 08:21 PM
Or is the violation having the equipment over the water pipe?
#115408 10/28/03 08:55 PM
I think a bigger problem might be the pipe above the panel from the looks of the rust on the outside of the panel and the trough under it. I popped a cover on one like this once and found two of the three fuses in the main rusted into the holders.
#115409 10/31/03 12:37 AM
K
Lots of problems here. Are those the right kind of straps, look like one hole EMT straps to me.
334.15 B (NM cable?) "shall be protected" is not met.