Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
[Linked Image]

[Linked Image]

[Linked Image]
Quote
About year ago someone started a thread about "Which is better, plastic or Steel?"

I came down squarely on the side of plastic and took some flak for it. My reasons were it does not rust, bust, or collect dust, or it does not deteriate as easily, and was easier fixed if damaged.

Naturally there were those that spoke of the strength of steel. I understand that argument, but my decision stands that I prefer plastic.

Last week, a building engineer at one of our schools was cleaning up behind one of our modular classrooms. When he moved some grass and leaves, he found this pipe. Rigid (not intermediate) that has been in a very long time. The conduit is completely separated, and you can see the conductors. The edges are sharp, and Lord help us in the event of a fault.
We have to schedule an outage to replace it WITH PVC.

The last pic shows the footer washed away under the brick, a non-electrical issue to be sure, but still ugly.

George C.

Joined: Jul 2002
Posts: 680
W
Member
So how long has the install been there and what if joe blow maintenance man hit a plastic riser with a lawn mower and it broke. Would you have to schedule a shut down to repair it right??. I'll take steel.

Joined: Jan 2003
Posts: 4,391
I
Moderator
I would replace it with steel, this is just my personal opinion.

I use plastic exclusively underground but I always break the surface with steel.

How long did it take to rust out like this?

We have no way of knowing if plastic would have lasted as long, for all we know that steel may have taken many hits with a lawn tractor and remained undamaged.

Service conductors in exposed plastic raceways scare me.

JMO, Bob

As a side note if I was getting this shut, down the disconnect and the trough look in tough shape too.

Why is one disconnect rustier than the other, they look identical (other than rust)????


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Aug 2001
Posts: 599
N
Member
The Ultimate in strength and corrosion protection!

Joined: Jun 2003
Posts: 681
P
Member
I myself like both PVC and Rigid, they both have their special uses.
What I would really like to see (but know it is unrealistic) is more preventative maintenance.
BTW - great pictures!

Pierre


Pierre Belarge
Joined: Apr 2002
Posts: 2,527
B
Moderator
For galvanized-rigid conduit, the points of transition from soil to air, concrete to soil or air to concrete are said to be most susceptible to corrosion.

I don't know of a reference to back this comment.

Joined: Jan 2003
Posts: 4,391
I
Moderator
Scott, I think your back up to that statement could be a look at any wood or steel pilings in water, they always rot out at the transition from water to air, both are need for decomposition.

Nick, we use that conduit or a type like it, on many jobs and you make a good point, one 10' stick of this would "fix" this service for a long time.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Oct 2002
Posts: 482
Z
Member
I have to agree with PCBelarge...each has it's own advantage and each has serious disadvantages. I prefer PVC underground, transitioning to metal a couple of inches above grade. This way, the only PVC exposed is usually the coupler, which is naturally thicker plastic and stronger. Metal, especially right near the ocean where most of my work is, WILL disolve eventually if in contact with the soil. You can bet on it.

I recently had an association community with pole lights fed from galv rigid that had corroded and collapsed UNDER ROADS in the community. We had to abandon those runs and route power from other sources, add pilasters, cut through 4" thick roots, etc.. My arms are still sore from all the trenching (in the middle of August, I might add)!

Joined: Sep 2003
Posts: 200
U
Member
Supposing PVC was used underground and transitioned to rigid or EMT a few inches above grade... how about pouring a concrete curb around it?

Joined: Oct 2000
Posts: 5,392
S
Member
[Linked Image from plastibond.com]

peanutbutter in my chocolate, chocolate in my peantbutter?


2 thumbs up Nick......


Link Copied to Clipboard