ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 255 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Picture a situation where 'City Water' has been brought into a House (copper line) and the old Well piping disconnected, but the Ground Wire has not been moved from it's original location. What are the issues, what should be done and why?

[Linked Image]

Joined: Apr 2002
Posts: 2,527
B
Moderator
One suggestion — Although the wellhead seal looks decidedly nonmetallic, there may be one good reason for connections to both the casing and new municipally-connected feed—a metal well casing often makes an outstanding grounding electrode. The old 6-inch casing at my rural house measured <2&#8486; with a three-point test, and that is often considered “utility-substation grade.” {The equally-old ‘driven’ ¾-inch-pipe electrode was 65&#937;.}

Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Remember now that the interior metal water piping is no longer connected to this well piping. What problems/issues does that present?

Bill


Bill
Joined: Aug 2002
Posts: 402
J
Member
Assuming there is no interconection between the old well head and the new city water a new bond needs to be added to the new water system.

Joined: Mar 2001
Posts: 345
T
Member
I would add a new grounding electrode conductor (GEC)to the new water utility entry piping. I would leave the present GEC in place. This would bond both systems to the main bonding conductor.
--
Tom


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Thanks,

What hazards, if any, exist with the way it is now? What would you tell the owner of this house?

Bill


Bill
Joined: Oct 2000
Posts: 5,392
S
Member
that the interior plumbing may be able to be energized due to a rusty bond...

Joined: Oct 2000
Posts: 5,392
S
Member
not as prevelant in this particular pix, the white powdery buidlup we sometimes see , similar to battery connections is explained by Mark Ode in an article Here