0 members (),
171
guests, and
31
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 3,682 Likes: 3
OP
Administrator Member
|
I've heard that the "loophole" that's allowed Alarm, Data, & other LV types to get away with coming in after-the-fact (inspections) to do their work is being closed with the 2002 NEC. Is this true??
Sure would be nice. We do our best to comply with the codes, and make a safe installation, only to have these guys come in and blow a hole the size of a small dog through a firewall to install their tiny cables after we're done. (These fellas were pretty sloppy, ehh?) Scott (Electure)
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
wiring is all the same to the general public, so these sorts give us all a bad name. I thought art 800 builds on the first 3 chaps. of the NEC, it does not exclude it as far as i have read ( but i read slow)
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Sparky, "Chapter 8 ... is independent of the other chapters except where they are speciffically referenced therein." 90-3
Don(resqcapt19)
Don(resqcapt19)
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
I'm actually glad to see this. I thought my company was the only place that looked like this!!
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Don; by golly it does say that! oh well... so much for neat & workmanlike !
|
|
|
|
Joined: Jun 2001
Posts: 642
Member
|
About time for that loop hole to be closed. Too many inspectors tell me that security, telco,and TV are not my area to inspect. Can see junk like this in just about every commercial building around here. much worse if there has been tenant changes.
ed
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
i hear rumor that it will
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
2002 NEC 760.2: Abandoned Fire Alarm Cable. Installed fire alarm cable that is not terminated at equipment other than a connector and not identified for future use with a tag.
760.3(A) Spread of Fire or Products of Combustion. Section 300.21. The accessible portion of abandoned fire alarm cables shall not be permitted to remain.
760.61(A) Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type FPLP. Abandoned cables shall not be permitted to remain. Types FPLP, FPLR, and FPL cables installed in compliance with 300.22 shall be permitted.
These new restrictions show up in other Chapter 7 and 8 articles.
Joe Tedesco, NEC Consultant
|
|
|