ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 394 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
[Linked Image]
Photo submitted by Joe Tedesco
Quote
Question: Is an expansion fitting required here?

Joined: Dec 2000
Posts: 4,294
Member
The answer to this is easier to find in the '99 NEC than the '96. The table for the expansion of PVC has been moved to Article 347 from an obscure spot in Chapter 9.
­ If that conduit is 4' long, and the temperature change is 130°, the answer would be no. (5.3"X.04=.212", which is less than 1/4")
However, if it's 5' long, with a 130° change in temp,5.3"X.05=.265", one would be required.

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Temperatures not withstanding, if frost heave is a problem, then an expansion fitting would be required. Look in the misc. section of the code, 300-5(j)

Tom


Few things are harder to put up with than the annoyance of a good example.
A
Anonymous
Unregistered
I wouldn't expect frost to be a problem if the conduit extends below the frost line.

The temperature change of the portion below ground is narrower.

Frost can heave inches in certain soils. A simple expansion joint won't solve that problem.

Joined: Dec 2000
Posts: 4,294
Member
Thanks, I never thought about that, being from So.CA. That's one thing that's so good about the BB, is that I'm able to learn about circumstances and reasons for other locations. (Is this what you guys were calling a "frosty"?) I just thought of the 130° as being a pretty extreme variance

Joined: Apr 2001
Posts: 507
G
Member
With the last code review our AHJ decided that all transitions from above or below grade must have expansion fittings. I have had to pull a direct buried service lateral and install a expansion joint when the pipe ended 18" below grade.

I agree that the expansion joint is a good idea when running continuos conduit.....but when direct burial is used, it's ridiculous