The answer to this is easier to find in the '99 NEC than the '96. The table for the expansion of PVC has been moved to Article 347 from an obscure spot in Chapter 9.
If that conduit is 4' long, and the temperature change is 130°, the answer would be no. (5.3"X.04=.212", which is less than 1/4")
However, if it's 5' long, with a 130° change in temp,5.3"X.05=.265", one would be required.