#111937 - 12/07/00 08:26 PM What's wrong with this Picture?
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3006
Loc: NY, USA

See what\'s wrong?

Click on Photo for a closer look

Note: Wirenuts were removed and are not part

of the violations under scrutiny here.

Comments?


Top
#111938 - 12/07/00 10:24 PM Re: What's wrong with this Picture?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2326
Loc: Williamsburg, West Virginia, U...
To start off with...

11 #12 Conductors in a box designed for 6 (assuming the box is 1-1/2" deep and not 1-1/4") Including the deduction for the clamps, there are 6 too many conductors in the box.

The box appears to be unsupported.
Scratch that... I see the bracket now...

The ground wires should be snipped off IF there is no "true" ground present in the box...OR if one of the 12-2-G wires is the feeder, the box isn't bonded properly.

The conductors do not have six inches of free length.

Are the cables stapled within 12 inches of the box? Doubtful, but inconclusive in the photo.

Less than 1/4" of jacket on th NM Cable in the box... (Some one told me that rule is only for plastic boxes...any comments?)

No Connector on the ground? (Crimp or wirenut) You did say that the wirenuts were removed, but the "ground" conductors don't appear to have the scars. (This same someone told me that twisting the grounding conductors together with no other means of connection is ok by code...sounds fishy to me...)

Was this protected at 15A or 20? There is one lone #14 Cable I believe...

That's about all I see...
_________________________
-Virgil

Top
#111939 - 12/08/00 05:43 AM Re: What's wrong with this Picture?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
Sparky,

Thanks for your Comments. There is at least 1 more thing that is fundamentally wrong here that you didn't see (Well, you did but you didn't realize it)

To Comment on your other Comments, they are pretty good. The location is in a basement so it may have been a porcelain fixture location at one time. I never heard the 1/4" jacket rule only being for plastic boxes unless they mean that it should be longer in other boxes such as this with clamps in which case I would say that the jacket should extend 1/4" further than the clamp. Maybe someone else has a comment on this?

Can you see anything else?

Top
#111940 - 12/08/00 12:58 PM Re: What's wrong with this Picture?
gpowellpec Offline
Member

Registered: 12/06/00
Posts: 128
Loc: Irving, Tx USA
Are the clamps upside down?

Top
#111941 - 12/08/00 02:20 PM Re: What's wrong with this Picture?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The white jacketed cable on the left in not correctly installed in the clamp, and I don't think you are permitted to place more than one cable under a single clamp.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#111942 - 12/08/00 04:19 PM Re: What's wrong with this Picture?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
Don,

You are probably right about the clamps. Do you know why they are shaped like they are though?

What I am looking for is something that is not only wrong, but it is totally the opposite of what it should be. (that's a hint)

Top
#111943 - 12/10/00 01:22 AM Re: What's wrong with this Picture?
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3006
Loc: NY, USA
Ok,

Here's another.. Hmm what was the name of that Chubby Checker song?

Top
#111944 - 12/10/00 09:24 AM Re: What's wrong with this Picture?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2326
Loc: Williamsburg, West Virginia, U...
The neutral wires are twisted in the wrong direction... (counter-clockwise). For that matter, I guess the hot wires were too.

Are the clamps designed for BX or other Cable?
_________________________
-Virgil

Top
#111945 - 12/11/00 05:14 AM Re: What's wrong with this Picture?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
Sparky,

Ding Ding Ding !! You got what I was looking for! I guess the Chubby Checker mention must have done it. When this box was opened the wirenut just about fell off the white wires. This occurrance is often accompanied by having tape wrapped around to hold it on.


The clamps came with the box I'm sure. I was wondering myself why they are shaped like they are and if a wire was allowed to be installed as the newer one on the left seems to be. I can see an advantage to putting the cable in this way if say an extension ring was added it would be easier to reach the wires. I don't think that the clamps are designed for Bx because there is no provision to retain the anti-short bushing on the cable.

Top
#111946 - 12/29/00 04:23 AM Re: What's wrong with this Picture?
LNP&S Offline
Junior Member

Registered: 12/29/00
Posts: 8
Loc: Colebrook, NH
Bill
As I remember some of these older boxes had the "romex" knockouts in the top as well as in the side allowing installation on the bottom of a floor joist and entry through the top of the box. I think the clamps were designed to accept cables either through the top or side knockouts - thus the rounded cable formations on top and side of the clamp.

Top
#111947 - 01/01/01 09:45 AM Re: What's wrong with this Picture?
Tom Offline
Member

Registered: 01/01/01
Posts: 1063
Loc: Shinnston, WV USA
Here in WV, this must be considered a state of the art junction box since I've seen so many just like it, or their close cousins.

By the way, just in case you can't see it, my tongue is firmly planted in my cheek.

Happy New Year to all.

[This message has been edited by Tom (edited 01-01-2001).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#111948 - 01/01/01 12:50 PM Re: What's wrong with this Picture?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2326
Loc: Williamsburg, West Virginia, U...
Yeah, I can vouch for that, Tom! It seems to be the standard J box for these parts; and you are allowed to put as many cables as you can force into it as well!
_________________________
-Virgil

Top
#111949 - 01/15/01 01:44 AM Re: What's wrong with this Picture?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2326
Loc: Williamsburg, West Virginia, U...
 Quote:
Originally posted by Bill Addiss:

I never heard the 1/4" jacket rule only being for plastic boxes unless they mean that it should be longer in other boxes such as this with clamps in which case I would say that the jacket should extend 1/4" further than the clamp. Maybe someone else has a comment on this?



Found an article by Charles R. Miller in the ECM Code in Focus. He points out that the 1/4" rule is in the section for NM boxes. In order to keep from plagiarizing, you can read it here and search under September 2000 Author Charles R. Miller.

Notice by the number of edits, I tried to make it easier...

Like the AC anti-short bushing and the anti-oxidant "rules", I wonder what other "codes" don't really exist?


[This message has been edited by sparky66wv (edited 01-15-2001).]

[This message has been edited by sparky66wv (edited 01-15-2001).]

[This message has been edited by sparky66wv (edited 01-15-2001).]
_________________________
-Virgil

Top
#111950 - 02/05/01 10:36 AM Re: What's wrong with this Picture?
exxon Offline
Junior Member

Registered: 02/04/01
Posts: 6
Loc: Fort Nelson , British Columbia...
Would also have been nice to see the 150mm of free conductor left in the box for splices , But I guess he wasn't finished running wires into the J.Box as he need the room .

Top
#111951 - 03/06/01 07:48 AM Re: What's wrong with this Picture?
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3977
Loc: Fullerton, CA USA
Those codes for anti-shorts, etc. do exist.
see 110-2, 110-3, 90-7. Installation to manufacturers specs. The cable I get comes with a bag of bushings attached right to it.