The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#111937 - 12/07/00 08:26 PM What's wrong with this Picture?
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3006
Loc: NY, USA

See what\'s wrong?

Click on Photo for a closer look

Note: Wirenuts were removed and are not part

of the violations under scrutiny here.

Comments?


Top
#111938 - 12/07/00 10:24 PM Re: What's wrong with this Picture?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2326
Loc: Williamsburg, West Virginia, U...
To start off with...

11 #12 Conductors in a box designed for 6 (assuming the box is 1-1/2" deep and not 1-1/4") Including the deduction for the clamps, there are 6 too many conductors in the box.

The box appears to be unsupported.
Scratch that... I see the bracket now...

The ground wires should be snipped off IF there is no "true" ground present in the box...OR if one of the 12-2-G wires is the feeder, the box isn't bonded properly.

The conductors do not have six inches of free length.

Are the cables stapled within 12 inches of the box? Doubtful, but inconclusive in the photo.

Less than 1/4" of jacket on th NM Cable in the box... (Some one told me that rule is only for plastic boxes...any comments?)

No Connector on the ground? (Crimp or wirenut) You did say that the wirenuts were removed, but the "ground" conductors don't appear to have the scars. (This same someone told me that twisting the grounding conductors together with no other means of connection is ok by code...sounds fishy to me...)

Was this protected at 15A or 20? There is one lone #14 Cable I believe...

That's about all I see...
_________________________
-Virgil

Top
#111939 - 12/08/00 05:43 AM Re: What's wrong with this Picture?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
Sparky,

Thanks for your Comments. There is at least 1 more thing that is fundamentally wrong here that you didn't see (Well, you did but you didn't realize it)

To Comment on your other Comments, they are pretty good. The location is in a basement so it may have been a porcelain fixture location at one time. I never heard the 1/4" jacket rule only being for plastic boxes unless they mean that it should be longer in other boxes such as this with clamps in which case I would say that the jacket should extend 1/4" further than the clamp. Maybe someone else has a comment on this?

Can you see anything else?

Top
#111940 - 12/08/00 12:58 PM Re: What's wrong with this Picture?
gpowellpec Offline
Member

Registered: 12/06/00
Posts: 128
Loc: Irving, Tx USA
Are the clamps upside down?

Top
#111941 - 12/08/00 02:20 PM Re: What's wrong with this Picture?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The white jacketed cable on the left in not correctly installed in the clamp, and I don't think you are permitted to place more than one cable under a single clamp.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#111942 - 12/08/00 04:19 PM Re: What's wrong with this Picture?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
Don,

You are probably right about the clamps. Do you know why they are shaped like they are though?

What I am looking for is something that is not only wrong, but it is totally the opposite of what it should be. (that's a hint)

Top
#111943 - 12/10/00 01:22 AM Re: What's wrong with this Picture?
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3006
Loc: NY, USA
Ok,

Here's another.. Hmm what was the name of that Chubby Checker song?

Top
#111944 - 12/10/00 09:24 AM Re: What's wrong with this Picture?
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2326
Loc: Williamsburg, West Virginia, U...
The neutral wires are twisted in the wrong direction... (counter-clockwise). For that matter, I guess the hot wires were too.

Are the clamps designed for BX or other Cable?
_________________________
-Virgil

Top
#111945 - 12/11/00 05:14 AM Re: What's wrong with this Picture?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4185
Loc: NY, USA
Sparky,

Ding Ding Ding !! You got what I was looking for! I guess the Chubby Checker mention must have done it. When this box was opened the wirenut just about fell off the white wires. This occurrance is often accompanied by having tape wrapped around to hold it on.


The clamps came with the box I'm sure. I was wondering myself why they are shaped like they are and if a wire was allowed to be installed as the newer one on the left seems to be. I can see an advantage to putting the cable in this way if say an extension ring was added it would be easier to reach the wires. I don't think that the clamps are designed for Bx because there is no provision to retain the anti-short bushing on the cable.

Top
#111946 - 12/29/00 04:23 AM Re: What's wrong with this Picture?
LNP&S Offline
Junior Member

Registered: 12/29/00
Posts: 8
Loc: Colebrook, NH
Bill
As I remember some of these older boxes had the "romex" knockouts in the top as well as in the side allowing installation on the bottom of a floor joist and entry through the top of the box. I think the clamps were designed to accept cables either through the top or side knockouts - thus the rounded cable formations on top and side of the clamp.

Top
Page 1 of 2 1 2 >



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals