ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 420 guests, and 16 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
#110990 08/14/06 11:44 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Quote
This is a service that a local handy man built. The major Code violation was the use of a fitting for liquid tight flexible conduit on rigid non metallic conduit.

Other than that it just looked like trash.

Alan Nadon
[Linked Image]

[Linked Image]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#110991 08/15/06 12:34 AM
Joined: Feb 2005
Posts: 693
L
Member
He should have used a second LB.

I agree, it's not pretty, but I've seen worse.

How would you have done it?


Larry Fine
Fine Electric Co.
fineelectricco.com
#110992 08/15/06 02:10 PM
Joined: May 2005
Posts: 178
J
Member
Couldn't you enter this type of meter base through the top using a Meyers hub?

I assume the window isn't functional.

#110993 08/15/06 02:50 PM
Joined: Oct 2005
Posts: 100
J
JJM Offline
Member
That meter pan is for UNDERGROUND service. How difficult would it have been to get the right meter pan for overhead service? The big box stores sell them for less than $50 and underground pans usually cost more, and aren't always in stock.

And it does look like trash too. Here they have a nice flat cinder block wall they could've used to mount the conduit to. Instead, they mount it to the uneven siding. Ugh!

Joe

#110994 08/15/06 08:06 PM
Joined: Nov 2000
Posts: 2,148
R
Member
It looks like there is a short piece of liquidtight conduit between the two liquidtight connectors.
Don


Don(resqcapt19)
#110995 08/15/06 08:19 PM
Joined: Feb 2004
Posts: 1,438
Member
Where I live the POCO would throw a clot the size of a pound cake over that LB being in there... LFMC in the mix would just make em all the more thrilled [Linked Image] RMC is all that PG&E allows for overhead (Along with most other CA POCO's I've dealt with)

#110996 08/15/06 09:11 PM
Joined: Jun 2005
Posts: 821
S
Member
Quote
How would you have done it?

A) I would have used the POCO specified meter can with the hub on the top, not on the bottom.

B) For where the service head is in the picture, service entrance cable would be the most practical installation IMO.

C) The best installation IMO would be up out of the top of the meter can with RNC, 90ยบ sweep to the left, 10' run to a pulling LL, then through the roof, install mast kit.

#110997 08/16/06 08:46 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Shock:
OK, I'll critique your way 'Jersey' style...

As to going 'thru the roof' 2-1/2" RGC is PSE&G required for a mast install. They also require 'permission' for condulets (LL)
on line side of meter, & with non-removable fastners on the cover.

Dependent on what's above the raw plywood soffit....you may be inside the structure?? Can't say for sure due to the picture angles.

SE Cable, may be way to go as you said.

John

PS: As Larry said, I also have seen worse!


John
#110998 08/16/06 10:50 PM
Joined: Dec 2004
Posts: 1,064
D
Member
Ok, I'll bite...

What is the code ref. for the liquidtite on the PVC?

#110999 08/16/06 11:19 PM
Joined: Jun 2005
Posts: 821
S
Member
John, It hadn't even occured to me using an LL on the line side is a no-no. Just didn't think of it. The window up there is also something to consider.

#111000 08/17/06 05:58 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Ron:
It's not a definite 'no-no'; permission is required. PS is still funny about that. Used to be 'to prevent unauthorized access to energized conductors, BEFORE the meter'.

A call to one of the PS Wiring Inspectors, and a quick site visit will get 'permission' if the condulet is the logical way to go.

John


John
#111001 08/17/06 10:03 PM
Joined: Jun 2005
Posts: 821
S
Member
Can't blame the POCO for not wanting to get robbed by a customer :-)

#111002 08/18/06 06:46 PM
Joined: Jul 2005
Posts: 49
V
Member
Ok, I agree that it looks bad but is there a code violation? I don't see one. I am guessing that the guy used a "liquidtite" connector becasue of the name, but they also used a FA before the connector. Odd yes, violation, don't think so. Just odd.


Pete
#111003 08/18/06 08:20 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
VA:
Based on the pics, and the comments above I THINK it's a FA to a straight ST Conn to a little pc of ST to the ST 90.

Violation?? Sorry to say there's nothing I could write a 'RED" for. Workmanship is not a 'RED" offense in NJ

ALAN:

As I described the meter end of the raceway, is that how it is?? Or, is that a pc of PVC btwn straight & 90??

John

[This message has been edited by HotLine1 (edited 08-18-2006).]


John
#111004 08/18/06 08:48 PM
Joined: Dec 2004
Posts: 1,064
D
Member
Alan, why did you tag it for the fittings?

Quote
The major Code violation was the use of a fitting for liquid tight flexible conduit on rigid non metallic conduit.

#111005 08/20/06 12:29 PM
Joined: Mar 2005
Posts: 399
A
Member
There was no seal tite going into the fitting. The nonmetallic connector was jammed into the 90' fitting.
NEC 110.3(B) applies.
Alan--
N.J electrician mentioned the key. They should have used a meter socket with a top hub and saved two of the 90's


Alan--
If it was easy, anyone could do it.
#111006 08/20/06 03:41 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
I have to say that when I zoom in on those fittings here is what I see from left to right.

PVC Female adapter, liquidtight straight connector with lock nut, a very short section of liquidtight, finally a liquidtight 90.

It looks ugly but code compliant in the picture.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#111007 08/20/06 03:50 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
[Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#111008 08/20/06 06:37 PM
Joined: Mar 2005
Posts: 399
A
Member
Studying the picture, you seem to be right, it has been too long for me to remember it exactly.
Alan--


Alan--
If it was easy, anyone could do it.
#111009 08/21/06 09:18 PM
Joined: Feb 2006
Posts: 7
A
Junior Member
Actually there is one thing keeping it from being water tight. Any guesses?

Allen

#111010 08/22/06 10:17 AM
Joined: Mar 2005
Posts: 399
A
Member
These are old pictures.
I had to go back and check why it was a violation at the time.
Section 230.43 before 1990 did not allow LTFC as a service raceway material. It was changed first to allow flex metal and then the next cycle they included LT.
Sometimes I get lost in the forest while looking for a tree.
Alan--


Alan--
If it was easy, anyone could do it.
#111011 08/22/06 11:15 AM
Joined: Feb 2005
Posts: 693
L
Member
" Actually there is one thing keeping it from being water tight. Any guesses?"

The locknut against the female adapter?


Larry Fine
Fine Electric Co.
fineelectricco.com
#111012 08/25/06 10:26 AM
Joined: Feb 2006
Posts: 7
A
Junior Member
Yes, and I believe you could fail this for that. Also it looks as though the strap at the top of the riser is broken or not attached. As ugly as it is, I don't see any other reason to fail.

Allen

#111013 09/19/06 10:05 PM
Joined: Oct 2002
Posts: 830
S
Member
Just breezing through the pictures and thought I would ask; Can handyman do this type of work without a license where this picture was taken? Just curious. Steve

#111014 09/21/06 09:39 PM
Joined: Sep 2006
Posts: 23
E
Member
Not in California. Services cannot be touched by anyone other than a C-10 holder
This is scary it looks like this guy used whatever was laying around his storage to hang this service including square head lags.

#111015 09/26/06 08:39 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
SparkyNC:
In New Jersey, single family resi, homeowner can do service or anything else electrically, as long as he/she owns & lives in it (with permit)
Other than that, multi family (>2), comm, etc has to be Lic. EC for service & everything else.

John


John
#111016 09/26/06 09:16 PM
Joined: Feb 2004
Posts: 1,438
Member
Quote
Not in California. Services cannot be touched by anyone other than a C-10 holder

Homeowners can pull their own permits and do their own work here in the Golden State as well... Panels and all.

#111017 10/12/06 09:41 PM
Joined: Oct 2002
Posts: 482
Z
Member
You could argue the violations all you want, and it may even pass inspection the way it is, but I can tell you right now that neither Southern California Electric or San Diego Gas and Electric PoCos that I work with here in OC California would ever let that fly. They would flat out refuse to hook it up. They are extreemly picky (and for good reason) on every bit of the run all the way up to their meter. I can see unacceptable radius on the 90s, not to mention the radius on the LT connector, and the LB would be questioned as well. Even if they don't have to pull the wire, they have the last word.

I seriously doubt they would even hook this up as a temp service for a work site meter.

#111018 10/15/06 01:50 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Quote
Homeowners can pull their own permits and do their own work here in the Golden State as well...

Randy, I have seen a few get denied at the permit counter here. And it is kinda funny and very serious few moments for me pulling my own permit, and having some HO at the next spot at the counter. I show all my paperwork, and I'm on my way.... The Electrical Inspection Dept here will send down the on-duty Inspector to quiz them about the whole job before or if they give them one. It's fun to watch, so I usually stick around..... (They do this for GC's too pulling a Permit for a service) If they dont answer the questions in satisfactory method, they wont give them a permit. And I have seen a few good blow-ups there at the counter because of it. I quietly applaud the Inspectors for it...

Anyway, back to the violation here: (This portion of the code has been deleted locally here)

Quote
230.43~(15) Flexible metal conduit not over 1.8 m (6 ft) long or liquidtight flexible metal conduit not over 1.8 m (6 ft) long between raceways, or between raceway and service equipment, with equipment bonding jumper routed with the flexible metal conduit or the liquidtight flexible metal conduit according to the provisions of 250.102(A), (B), (C), and (E)
(16) Liquidtight flexible nonmetallic conduit
Where flexible metal conduit or liquidtight flexible metal conduit is installed for services, a bonding jumper must be installed between both ends within the raceway. The bonding jumper is allowed to be installed outside the raceway, but it must follow the path of the raceway and cannot exceed 6 ft in length. The bonding jumper must not be wrapped or spiraled around the flexible conduit.

I dont see where that Flex is bonded on both ends....

[This message has been edited by e57 (edited 10-15-2006).]