From Sierra-Electrician (aka Rob) A real nice find in Sunnyvale, CA This 2" run is from a separate metered service, it passes through this service and goes under ground with no connector to the PVC...as if that matters. The service it passes through was installed 3 years ago and was inspected.
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
ARE LIVE BUSS BARS DOWN THERE!?!?! Is that metal raceway? Or is that just a neutral/ground buss and/or plastic raceway? That looks real scarey!
|
|
|
|
Joined: Feb 2005
Posts: 219
Member
|
Its a Sq D I-Line M/M + Dist, the busing you see is the "A", "B" & "C" phases. Its 120/208V 3P, 4W. The raceway is 2" alum flex secured with ty-raps to the gear structure. There is about 1" clearance between the conduit and the bussing.
Rob
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
I just had a (one) beer...it must have been exceptionally potent- I think I see where someone snaked flex through some switchgear, right along some hot busbars.
This cannot possibly be the case- no one can be thet ignorant / stupid / daring / lucky.
Either that, or it is special "Bangalore" flex.
|
|
|
|
Joined: Dec 2004
Posts: 354
Member
|
Would it be corect to assume that whoever installed the 2" run could lose their license ?
|
|
|
|
Joined: Aug 2005
Posts: 24
Member
|
Why bother with the flex in the first place? At least if the raw THHN's were exposed in there it would be safe. However I remember anything entering a panel must terminate there as well?
|
|
|
|
Joined: Dec 2005
Posts: 869 Likes: 4
Member
|
Is that flex conduit metallic or plastic ?
Whichever clown who installed that conduit, must have used 8 out of it's 9 lives.
If that conduit is metal, that's illegal to run it across live busbars in such close proximity without any form of insulating shielding.
The product of rotation, excitation and flux produces electricty.
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Nah Ray, It looks like that cheap stuff we used to get here for Air Con installs. Half the quality of Betta-flex and easily crushed by an over-tightened cable tie. Even Vacuum cleaner hoses have more mechanical strength.
|
|
|
|
Joined: Apr 2003
Posts: 60
Member
|
From Sierra Electrician The raceway is 2" alum flex secured with ty-raps to the gear structure. There is about 1" clearance between the conduit and the bussing. Sure looks like flex when it makes that bend and goes upward at the side of the enclosure. RUN away, very far away! Edited to fix UBB [This message has been edited by CaOperator (edited 06-02-2006).]
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
These are easily the most terrifying pics I've seen on ECN.
Flex can be a dangerous raceway in the hands of the insane.