as some of you know here on the forum, nearly all of our work is related to the public house, nightclub and liesure industry.
personally i would not, or any of my crew, leave an installation in such a bad condition, temporary or not.
that is just not done, the lack of MCB blanks is one thing butjust the condition of the instalaltion raises more questions.
Pic # 2, appears to be a Wylex MCB board with maybe one 32A MCB and alot of lighting circuits connected, fed via what appears to be a bit of 10mm T/WE (twin and Earth similar to romex, the cable colours are the new harmonised type,
Is the BD staying or is it going, you could place all of those circuits on the main DB (the memsheild 2 board.
the SWA connected tot he Joint box, i would be worried about even opening that can of worms.!
pic # 3, the suspended RCD, well there aint a lot to say really about that one just, WHY??
pic # 5, the connection of cables to the lower TPN MCB, was the guy just lazy or does he like to test circuits energised by placing huis test equipment onto the exposed portion of the conductor entering the MCB ?
Earthing, this does not appear to be within code, 16mm tails incoming 10mm out, i dont think so!
main earth connection shall be the same diameter as the main supply feeds.
the thing in the US of `flying splices` well this just takes the biscuit, i would in no way shape or form leave this service enrgised in this condition.
temporary or not, it is just an absolute mess, especially as the property is occupied by customers and staff !!
frightening, very frightening .....
i hope that this instalaltion is going to re done soon, very soon..
Britspark