Found this service with the neutral and phase conductors reversed in the meter base while performing a final inspection on a single family dwelling.
- necbuff
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#107738 08/03/04 01:39 AM
Aside from the darwin award for not even being able to wire a meter socket, Please tell me thats not a bare AL ground wire going right in front of the main lugs for the panel?!?!?!? [Linked Image]
-Randy
[This message has been edited by Lostazhell (edited 08-03-2004).]
#107739 08/03/04 02:05 AM
I think most 3 year-olds can match colors better than that. Things we do totally without concious thought are far beyond some people.
#107740 08/03/04 03:05 AM
Good panel, sloppy "work".
#107741 08/03/04 03:16 AM
e57 Offline
Is this service live?!!!!
No ground or bond between the meter and main, so the main case and neutral is 120, and one phase 0, the other 220?
Looks like some smoke damage there on the riser neutral?
This may not have happened if this person hadn't gone through all the "red tape" getting it inspected. Nice catch, and a real good thing you looked!
#107742 08/03/04 01:41 PM
The GEC in pipe is nice although I dont understand the gap between end of pipe and meter can.
#107743 08/03/04 09:59 PM
Service not energized, I am AHJ and I obviously rejected this one. That is an insulated conductor in front of the lugs and the reason for the gap is for other utilites to have a spot to hit the GEC for their service, eg; catv, phone.