ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 506 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#107704 08/12/04 08:35 AM
Joined: Dec 2000
Posts: 4,294
Member
Quote
came across this ground bar in a otherwise normal & clean looking panel... I didn't make a huge issue of it to the owner of the store, but I did note it in the contract.....

Randy


[Linked Image]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#107705 08/12/04 12:09 PM
Joined: May 2004
Posts: 162
C
Member
Are those sheetmetal screws w/washers??

looks a little shakey 250.8 maybe 110.3 (B)??

#107706 08/12/04 12:27 PM
Joined: May 2003
Posts: 1,158
Member
those screws are called Wafer teks they are all in in , I would use them mounting boxes to steel studding.

#107707 08/12/04 12:31 PM
Joined: Feb 2002
Posts: 840
C
Member
Looks like a GE ground bar in a Cutler Hammer panel. Not quite compatible.

Peter


Peter
#107708 08/12/04 06:01 PM
Joined: Jul 2004
Posts: 41
N
Member
I don't believe this installation is code compliant. Sheet metal screws are not permitted to connect grounding conductors to enclosures. 250.8........... In this case, tek (self tapping) screws.


Kenny Wilee
#107709 08/12/04 07:13 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Is it me, or does that bar look like it was cut in half for some reason?

If so both are a no-go.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#107710 08/12/04 08:47 PM
Joined: Nov 2003
Posts: 127
S
Member
Quote
Is it me, or does that bar look like it was cut in half for some reason?

Hmmm... split busses are BAD NEWS any way you look at them!!!!!!!

I just could not resist...!


No wire bias here- I'm standing on neutral ground.
#107711 08/13/04 01:13 AM
Joined: Sep 2002
Posts: 943
Likes: 2
N
Member
IMO, GE has the worst ground bars around, that split is "normal" for them.

#107712 08/13/04 05:43 AM
Joined: Jun 2003
Posts: 681
P
Member
This poses an interesting situation for inspectors.
Do we violate the installation for not using the proper listed equipment for the enclosure, or do we say at least they separated the equipment grounds from the neutral so I am satisfied?
This is a very typical installation I see almost everyday.
This is clearly a violation of 110.3(B), but...

I will say this; I have seen large faults where the connection of the fittings and the screws were scortched - obviously not a good sign for the fault current path.

Pierre


Pierre Belarge
#107713 08/13/04 03:46 PM
Joined: Feb 2004
Posts: 1,438
Member
110.3(B) is the first thing that came to mind with me when I saw this also... The thing I mostly was concerned about was that the panel can is being used as the bonding means (No separate EGC coming in with the feeders via EMT). If it comes down to clearing a fault on the 60A 240V A/C circuit which is connected in this panel, will the buttonheads or wafer teks be reliable in doing so?

Could this technically fall under 250.8?

-Randy

-Randy


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5