#107699 08/12/04 05:56 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Here is the original thread for the meter enclosure:

https://www.electrical-contractor.net/ubb/Forum2/HTML/001330.html


Ryan Jackson,
Salt Lake City
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#107700 08/13/04 02:21 PM
Joined: Feb 2004
Posts: 1,438
Member
Bob,
110.11 for the runoff thats undoubtedly entering this with the missing cover..
110.26(F)(2) for lack of protection from the sprinklers & lack of a "suitable enclosure"
314.15(A) for not placing this to prevent moisture from entering & accumulating in the box..
300.6(B) for the box in direct contact with the earth, someone posted pics in another thread of some buried Bell boxes.. I can't find the link right now...

-Randy

#107701 08/13/04 05:10 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Pretty Cool Randy.

110.11 I think is a stretch, the equipment is listed for outdoor use.

I do not see how you can apply 110.26(F)(2) to this outlet, if you do you will also have to apply all sections of 110.26 to all outlets and switches.

This would make kitchen counter outlets a violation of the work space requirements for example.

You defiantly got me with 314.15(A) [Linked Image], IMO that is right on the money, I will not forget that section now, Thank you. [Linked Image]

300.6(B) Allows boxes to be in direct contact with the earth "where made of material judged suitable for the condition, or where provided with corrosion protection approved for the condition."

Around here Bell boxes are judged suitable for dirt water etc.

I guess that is an AHJ call. [Linked Image]

I agree red tag with 314.15(A) on it.

Bob

[This message has been edited by iwire (edited 08-13-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#107702 08/13/04 05:20 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
We both forgot 406.8(B) for the in use cover.

This was probably in compliance when installed and there is no 'maintenance code' right now, so whata ya gonna do? [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#107703 08/13/04 05:44 PM
Joined: Feb 2004
Posts: 1,438
Member
I quoted 110.11 because there is no cover on the GFCI.. Considering the greenery in the picture, I'd bet the GFCI face is exposed to water at least every other day via the sprinkers & the GFCI itself isn't identified for the wet enviroment

I'll go with you on 110.26(F)(2).. I was thinking of the sprinkers as "leakage from piping systems" [Linked Image] (I tried!) & the fact that without the cover it's not a "suitable enclosure"

As far as 300.6(B), I'd be hard pressed to place an aluminum box in contact with the earth.. I can see moisture in the soil deteriorating it double time & eating it away... JMO, I always use PVC for anything in the ground when I can..

406.8(B)(1)... Thats where that is! [Linked Image] [Linked Image] [Linked Image]

-Randy