#107323 10/05/04 09:31 PM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
Photos by Dave55:

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#107324 10/05/04 10:36 PM
Joined: Jan 2004
Posts: 105
C
Member
aww... you should have taken some "before" pictures too

#107325 10/05/04 11:10 PM
Joined: May 2004
Posts: 697
D
Member
This IS the "before" pictures!!! Can't you tell that crack in the second picture needs to be caulked?

This is a very typical service in my neighborhood. The vertical conduit ran through a concrete pad. When the pad settled it pulled the conduit out of the meter socket. I did a service across the street last year that had done the same thing.

The distribution panel is a Federal Pacific. The electrical contractor saved where he could, as breakers were available at the time.

This was a pretty good job except the commute was a killer (90 seconds).

I was going to post some "after" pictures, but I'm not sure I want the vultures picking on my bones.

Dave

#107326 10/06/04 07:51 AM
Joined: Dec 2000
Posts: 4,294
Member
Hi Dave,
What's the white wire coming from the top right switch down to the neutral bar for?? (4th picture). [Linked Image]

#107327 10/06/04 09:10 AM
Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
That's not a neutral for a GFCI is it,
Electure?.
Just a wild guess.

#107328 10/06/04 08:01 PM
Joined: May 2004
Posts: 697
D
Member
That's two different wires, guys. It does look like one, but they must cross on the right to look like one. The upper connection was a 240 volt circuit for the clothes dryer.

Dave

#107329 10/07/04 01:43 AM
Joined: Feb 2003
Posts: 687
A
Member
The pipes pill out of the meters around here too. They say with groung freezing things can move around a bit. Plus not compacting the soil. We take those uot and put in a underground pedistal.

Besides the meter did you pass your inspection Dave? Doesent anything pass in Crystal Lake?

Tom

#107330 10/08/04 12:11 AM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
2 more from Dave:

[Linked Image]

[Linked Image]

#107331 10/08/04 04:11 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Is that a new idea on phase id? Black, black, black, black, black, black, red, red.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#107332 10/08/04 06:47 AM
Joined: May 2004
Posts: 697
D
Member
My work passes everywhere,Tom, doesn't yours? The colors are the different wire guages.

Dave

#107333 10/08/04 08:32 PM
Joined: Aug 2002
Posts: 402
J
Member
I personally don't like the tie wraps. It looks nice but hard to change a wire later on.

#107334 10/08/04 08:58 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Dave, the panel with the phasing issue wouldn't fly here. It would have to be A - B, (black - red) left to right, top to bottom. Service, feeder, and branch circuits. It's really common requirement in most areas. So all A phase black, all B phase red. Even two wire circuits.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#107335 10/08/04 11:21 PM
Joined: Apr 2001
Posts: 449
F
Member
Nice job, Dave. I'd be in trouble e57. I pull thwn in emt for a lot of my homeruns and I use red, black, yellow, pink, purple, orange, blue and brown for circuit ID purposes. Phase ID here only applies to the line side conductors(feeder/SE) of a panel whether they are 3 phase or single phase.

#107336 10/09/04 05:45 PM
Joined: Jan 2002
Posts: 1,457
E
Member
Looks good. I too would skip the ty wraps. What are you guys talking about "phasing issue"?

#107337 10/09/04 06:02 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
It's not NEC, but common practice. For us in SF it is required to phase all circuits. This is an example of our local code.

Quote


210-5(c). Add the following new section:





(c)Ungrounded Conductors. Underground conductor insulation shall be color coded as follows:



(1)One-hundred-twenty/two-hundred-forty-volt 3-wire circuits - “A” phase black, “B” phase red; 120/208 volt 4-wire 3-phase wye circuits - “A” phase black, “B” phase red, “C” phase blue; 120/240 volt 3-phase delta circuits - “A” phase black, “B” (high leg) phase purple, “C” phase red; 277/480 volt 4-wire 3-phase wye circuits - “A” phase brown, “B” phase orange, “C” phase yellow.


(2)Conductors for switch legs may be of a different color than the phase conductor other than green, white or gray when suitably identified at pull, junction and outlet boxes with marking tape, tagging or other equally effective means.





(3)Conductor insulation shall contain the applicable color pigment for circuit wire #14 AWG through #10 AWG. Ungrounded conductors #8 AWG and larger and ungrounded conductors of any size in cable assemblies may be pigmented colors other than green, white or gray, provided they are suitably identified at pull, junction and outlet boxes with marking tape, tagging or other equally effective means.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#107338 10/09/04 08:51 PM
Joined: Apr 2002
Posts: 558
C
Member
Mark, since this is a single phase system all conductors would need to be either black or red the way I read the SF code. There isn’t an A and B phase. When you install NM cable are you required to change the black wires to red in just the panel or every box they run to?

I actually like using ty-wraps but only a couple per side. They are easy to cut off later if needed.

Curt


Curt Swartz
#107339 10/09/04 10:35 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Yes, on the panel, raceway, and boxes. I usually try to pull only 3-wire to panels so it's not that bad, and use the red in the first box until they seperate. Same idea for 4-wire.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#107340 10/10/04 10:08 AM
Joined: Sep 2003
Posts: 650
W
Member
You'd think that in a market as large as San Francisco, that someone would be making up NM with Red/White/Bare.

-Jon

#107341 10/10/04 12:20 PM
Joined: Jun 2004
Posts: 206
C
Member
Dave, nice job. Gives new meaning to 110.12.

#107342 10/10/04 12:24 PM
Joined: May 2004
Posts: 697
D
Member
Thanks capt al, I was just about to state my regrets on posting after pictures to a tough audience.

Dave

#107343 10/10/04 01:56 PM
Joined: Jun 2003
Posts: 1,143
D
Member
Purty job, Dave!

I like the way nylocks (ty-wraps)look for new panels, but agree as a remodel guy they can be a pain.

It's still better than the average rat's nest of wire we all see.

#107344 10/10/04 02:01 PM
Joined: Dec 2003
Posts: 59
B
Member
nice looking job

#107345 10/11/04 08:57 PM
Joined: May 2004
Posts: 697
D
Member
We go by the NEC here regarding wire colors. My generous use of wire ties comes from my background in wiring machine controls. I used stranded wire on this job which doesn't stay put very well. I also do a lot of remodeling and could remove all these ties in a minute.

Dave

P.S. Some final comments before we let this thread die are:

I used a 2" nipple even though it's only 100-amp in case it got changed out later to a 200-amp service, which are getting more common here. I used duct seal in the nipple after taking this picture.

I plugged the four mounting holes with fender washers even though the holes aren't quite as large as a 1/2" knockout.

#107346 10/12/04 09:47 AM
Joined: Nov 2002
Posts: 558
G
Member
Nice looking job Dave. [Linked Image]


Russell

#107347 10/15/04 12:30 AM
Joined: Aug 2003
Posts: 57
Member
Looks good! I like seeing 'before' and 'after' pics of just about anything. Amazing. This really looks better. [Linked Image]


"Live the dream, you only get one chance."
#107348 10/15/04 10:51 AM
Joined: Nov 2001
Posts: 745
M
Member
Dave: I'll agree; it is a very nice looking job. More installs should look this good!

I'm interested in the construction of the service to the meter outside, since I have never seen such an install in my part of the country. With the bottom end of the raceway buried below ground level (and in contact with the ground), what do think it's life expectancy will be? Also, Is there somewhere a transition from UG conduit to this raceway, and where does it take place? Just curious...

Mike (mamills)

#107349 10/15/04 12:27 PM
Joined: May 2004
Posts: 697
D
Member
This is a typical installation around here, Mike. The service is underground and the POCO brings in a triplex (direct burial) into this pedestal type meter-socket. This meter-socket is essentially back-to-back with the distribution panel in the attached garage. A more typical installation in this area would probably be into a full basement, where you would need a 90 degree sweep into the distribution panel. Often the services are overhead rather than underground.

Dave

(edit) PS I've dug up these pedestal type meter-sockets that were installed 30-40 years ago and they're still in good shape. The paint may not look good, but there are no holes in the metal.

[This message has been edited by Dave55 (edited 10-15-2004).]