#106975 11/15/00 10:23 AM
Joined: Oct 2000
Posts: 3,682
Likes: 3
Admin Offline OP
Administrator
Member
<p align="center"> <img border="0" src=&q...t;400" height="266">

Click Photo for Closer Look
<blockquote>
<p align="center">Submitted by <a href="mailto:Bill@Electrical-Contractor.net">Bill Addiss

</a>This was found recently when renovating a Bathroom. The wire you see was attached to the device strap by some form of epoxy. Strange thing was, there was a Neutral in the box. The "Electrician" obviously didn't know
enough to use it.
</blockquote>

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#106976 11/28/00 08:39 AM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
This is a further explanation for those not familiar with this violation.

This type of device (switch/outlet combo) is something that is seen quite a bit in areas where it shouldn't be. In Bathrooms and Garages that didn't come with outlets, many of these devices have been added by simply replacing the switch. There MUST BE A NEUTRAL present and connected to the outlet portion of this device. If you don't know what that means and the Hazards involved, you should definitely not be doing any Electrical work!! These are also areas that should be under the protection of a GFCI, either in the device itself (switch/GFCI combo) or the circuit breaker (GFCI breaker).

Secondly, of concern is that, in these areas a dedicated circuit is often called for and that means that the outlet should not be hooked up with anything else, especially the lights. The outlet in a bathroom is supposed to be GFCI protected and on a seperate 20amp circuit breaker. That also means a larger wire size. This is to accomodate the very high wattage of today's Hairdryers. 1875 watts is roughly 16 amps, a typical circuit is only 15 amps. Common uses of this device in Garages are for plugging in an extra Refrigerator/Freezer or for the use of some power tools in a makeshift workshop. Once again, this is an area that needs GFCI protection and really should be on a different or separate circuit to prevent overloading and damage to the equipment being used on that circuit.


Bill
#106977 11/30/00 01:26 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
So many safety assumptions are made by the general public (the "handyman", etc.)for instance, an AWG 16 lamp extension cord can safely handle a microwave, a coffee pot and a toaster... simply because there are three receptacles at the end of the cord...

Or... if a breaker or fuse opens when your emglo compressor fires up... put a 30A on it..

Or... LXW boxes can handle 4 #10-3-G NM Cables because there are four holes...

Or... Neutral and ground are the same thing...like a chassis ground on a car, right...?

It never ceases to amaze me the things we run into... And, thank goodness, were discovered before harm was done.


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#106978 03/03/01 04:21 AM
Joined: Feb 2001
Posts: 54
T
Member
I ran into something like this in a buddy's kitchen, was an old house and there was an outlet next to the door, I was told that they could only use the outlet when the light was on. So if you had the light on, and then plugged something in, the lamp would get real dim....... Apparently it had once been part of a 3- way switch......Homewowners.....lol